[Equest-users] Window6 eQUEST Results
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Thu Apr 28 07:38:37 PDT 2011
Otto -
Re: baseline strategy - what you describe used to be our strategy as well (selecting the window that was closest from the library).
However, on LEED projects, a number of reviewers took issue with that approach, and requested that our models match the u-val and SHGC of the standard exactly.
We often define baseline windows using the simplified method to match the standard.
One of the caveats with the "close as possible" library approach is that ASHRAE hasn't released specific spectral / angular performance curves for the baseline glass ...
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto Schwieterman
Sent: Thursday, April 28, 2011 10:33 AM
To: Bruce Easterbrook
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Window6 eQUEST Results
Thanks Bruce,
I ended up selecting a window in the eQUEST library that was very similar to the results that I got from Window6.
What are others doing for creating their windows in eQUEST? Are you selecting the window from the library that is the most similar to the window that you are using? Are you importing the glass from Window6 or are you creating the window in eQUEST?
What are you using for the ASHRAE 90.1 baseline window? I typically select the window from the library that is the closest to the baseline window values.
From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
Sent: Thursday, April 28, 2011 10:28 AM
To: Otto Schwieterman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Window6 eQUEST Results
eQuest treats the glass and the frame as separate items. They are totally different thermodynamically. There is much more to window glass than just insulation value. I normally create windows and frames inside eQuest. You could then just check with window6 to confirm your overall value. I don't believe many people are having success importing window data from other programs.
Bruce Easterbrook P.Eng.
Abode Engineering
On 28/04/2011 09:23 AM, Otto Schwieterman wrote:
Hello everyone,
I created a window using Window6 and the results appear to be correct but when I import it into eQUEST the frame does not appear to import. The total window U-Value in eQUEST is 0.25 which makes sense if it does not include the frame but the results from Window6 shows a complete U-Value of 0.434.
Any help is appreciated.
Otto
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110428/9df292eb/attachment-0002.htm>
More information about the Equest-users
mailing list