[Equest-users] CHW error message
Chris Lowen
CLowen at glumac.com
Thu Dec 15 15:21:32 PST 2011
James -
I've had some luck getting around this one by applying reset schedules to the chilled water loop supply temperature so the "Design CHW Temp" defined on the "Basic Specifications" tab meets the 6 degree difference requirement, and then on the "Controls" tab set up a reset schedule that will reset the temperature of the chilled water loop to what you actually want the system running at.
Cheers
Chris
Chris Lowen
Energy Analyst
LEED AP BD+C
[cid:image001.gif at 01CCBB3A.9CB2E9D0]<http://www.glumac.com/>
________________________________
[cid:image002.jpg at 01CCBB3A.9CB2E9D0]
1325 - 4th Avenue, Suite 1515
Seattle, WA 98101
T. 206.262.1010 F. 206.262.9865
Thinking. Inside the building.
[cid:image003.png at 01CCBB3A.9CB2E9D0] <http://twitter.com/GlumacEngineers> [cid:image004.gif at 01CCBB3A.9CB2E9D0] <http://www.linkedin.com/company/34034?trk=tyah>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Thursday, December 15, 2011 2:43 PM
To: thomasv at iit.edu; Robby Oylear
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] CHW error message
Does anyone know if there is a way to bypass or ignore this error? I've worked on a few projects recently where we've been able to get close to a 46 degree LAT from an AHU with 42 degree water. Not a big deal I guess, but it would be nice to be able to be only 4 degrees above CHW temp.
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com<http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Varkie C Thomas
Sent: Thursday, December 15, 2011 5:44 PM
To: Robby Oylear
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] CHW error message
Robby: This project is being done by an architect who used DD. I looked for the error in CHW plant and forgot to look at HVAC supply temps. I was mistaken, the Detailed Edit does allow you to set CHWS temp but not SD and DD. Varkie
----- Original Message -----
From: Robby Oylear <robbyoylear at gmail.com<mailto:robbyoylear at gmail.com>>
Date: Thursday, December 15, 2011 4:29 pm
Subject: Re: RE: [Equest-users] CHW error message
> Whoops, here's the image I meant to send with the detailed edit
> screen:[image: image.png]
>
> On Thu, Dec 15, 2011 at 2:29 PM, Robby Oylear
> <robbyoylear at gmail.com<mailto:robbyoylear at gmail.com>> wrote:
>
> > Varkie,
> >
> > On wizard screen 3 of 3 under "CHW Plant Equipment" the setpoint is
> > defined. The default is 44 deg F.
> >
> > [image: image.png]
> >
> > In detailed edit mode this setpoint can be seen on the
> "Circulation Loop
> > Properties" screen:
> > [image: image.png]
> >
> > On Thu, Dec 15, 2011 at 2:22 PM, Varkie C Thomas
> <thomasv at iit.edu<mailto:thomasv at iit.edu>> wrote:
> >
> >> Kelsey, Robby,
> >>
> >> Thanks. The supply air temp was too low. What CHWS temp does
> eQUEST>> assume? This should be an input value too, besides temp
> rise.>>
> >> Varkie
> >> **
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/8eec8add/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 6582 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/8eec8add/attachment-0004.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 11793 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/8eec8add/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1800 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/8eec8add/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.gif
Type: image/gif
Size: 265 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/8eec8add/attachment-0005.gif>
More information about the Equest-users
mailing list