[Equest-users] Unmet Hours

Brad Robinson brad.robinson at yahoo.com
Thu Jul 7 08:15:32 PDT 2011


Hmmm..

Does that mean you need to sum the unmet hours of ALL separate systems as well?

In regards to the unmet cooling, LEED NC-2009 (Canada) notes that it is acceptable to have unmet cooling hours.  I interpreted this to mean that the unmet hours of concern are only on the heating side, not the cooling.



________________________________
From: "Patrick J. O'Leary, Jr." <poleary1969 at gmail.com>
To: Brad Robinson <brad.robinson at yahoo.com>
Cc: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Thursday, July 7, 2011 10:56:08 AM
Subject: Re: [Equest-users] Unmet Hours


 that would be 500 unmet hours.

the bigger leed review problem i've had is when i have more unmet hours
in one category in the proposed (like 200 unmet in cooling) and fewer
unmet hours in the other (like 0 in heating) but the baseline is
opposite.  certain leed reviewers think this is a problem.  the 90.1
requirement addresses the unmet hours per the entire building design
(both heating and cooling) not heating and cooling individually.

On 7/7/11 7:49 AM, Brad Robinson wrote: 
For LEED compliance under ASHRAE 90.1, are the 300 unmet hours
the sum of all the unmet hours in each zone, or the peak per zone?  In
other words if I have 250 unmet hours in one zone and 250 unmet hours
in another zone, does this comply, or is it considered 500 unmet hours
total?  By zones, I mean thermal zones served by the same air handling
unit.  Thanks.
>
>
>
>Brad Robinson
>
>
>
_______________________________________________
Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110707/2c67eb62/attachment-0002.htm>


More information about the Equest-users mailing list