[Equest-users] eQUEST Sunspace
Jackson, Alan
ajackson at klingstubbins.com
Thu Jul 7 13:03:15 PDT 2011
Have you tried reverse laying the interior wall? If the interior wall was defined in the sunspace, then the material layer is reversed where the interior material is layer on the sunspace side and exterior is on the interior zone side.
O |<-GLASS [ S ] INT-SURFACE->||<-EXT-SURFACE [ I ]
U | [ U ] || [ N ]
T | [ N ] || [ T ]
D | [ S ] || [ . ]
O | [ P ] || [ Z ]
O | [ A ] || [ O ]
R | [ C ] || [ N ]
|<-GLASS [ E ] INT-SURFACE->||<-EXT-SURFACE [ E ]
So let's say your interior wall was brick faced. The brick surface would actually be the interior layer where normally it would be the exterior layer on a standard wall exposure. Put simpler “inside” is the side in the space in which the wall was defined.
See if that helps.
Alan Jackson, LEED AP
KlingStubbins
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ercoli, Christopher
Sent: Thursday, July 07, 2011 2:16 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQUEST Sunspace
Has anyone in the group used the sunspace option in eQUEST? I have tried it and it blew up in LOADS Following is the .inp description of the Sunspace:
"EL1 North Perim Spc (G.N1)" = SPACE
X = -25.25
Y = 109.6
AZIMUTH = 51.024
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "EL1 Bldg Occup Sch"
LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
EQUIP-SCHEDULE = ( "EL1 Bldg Misc Sch", "EL1 Bldg OffEq Sch",
"EL1 Bldg OffEq Sch" )
INF-SCHEDULE = "ZG1-S1 (UVT) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0563044
PEOPLE-HG-LAT = 217.268
PEOPLE-HG-SENS = 250
LIGHTING-W/AREA = ( 1.14175 )
EQUIPMENT-W/AREA = ( 0, 0, 0.791 )
SUNSPACE = YES
AREA/PERSON = 165.463
POLYGON = "EL1 Space Polygon 1"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Office (Executive/Private) (79%)*
..
"EL1 North Wall (G.N1.E1)" = EXTERIOR-WALL
CONSTRUCTION = "EL1 EWall Construction"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"EL1 North Win (G.N1.E1.W1)" = WINDOW
GLASS-TYPE = "EL1 Window Type #1 GT"
FRAME-WIDTH = 0.108333
X = 0.808333
Y = 0.938333
HEIGHT = 7.17333
WIDTH = 138.803
FRAME-CONDUCT = 1.306
SPACER-TYPE = INSULATED
..
"EL1 SW Wall (G.N1.I1)" = INTERIOR-WALL
NEXT-TO = "EL1 WNW Perim Spc (G.WNW4)"
CONSTRUCTION = "Sunspace Wall construction"
LOCATION = SPACE-V1
..
"EL1 South Wall (G.N1.I2)" = INTERIOR-WALL
NEXT-TO = "EL1 Core Spc (G.C5)"
CONSTRUCTION = "Sunspace Wall construction"
INT-WALL-TYPE = STANDARD
LOCATION = SPACE-V2
..
"Sunspace Window" = WINDOW
GLASS-TYPE = "EL1 Window Type #1 GT"
X = 1
Y = 6.5
HEIGHT = 2
WIDTH = 122
C-WELL-HEIGHT = 6.5
C-WELL-WIDTH = 1
..
"EL1 SSE Wall (G.N1.I3)" = INTERIOR-WALL
NEXT-TO = "EL1 SE Perim Spc (G.SE2)"
CONSTRUCTION = "Sunspace Wall construction"
LOCATION = SPACE-V3
..
"EL1 Ceiling (G.N1.I4)" = INTERIOR-WALL
NEXT-TO = "EL1 North Perim Plnm (G.N6)"
CONSTRUCTION = "Air Ceiling of Sunspace"
INT-WALL-TYPE = AIR
LOCATION = TOP
..
"EL1 Flr (G.N1.U1)" = UNDERGROUND-WALL
CONSTRUCTION = "EL1 UFCons (G.N1.U2)"
LOCATION = BOTTOM
..
Following is the system description of the sunspace:
"EL1 North Perim Zn (G.N1)" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 1
BASEBOARD-RATING = -25605.4
FLOW/AREA = 0.25
OA-FLOW/PER = 18.2732
SS-FLOW-T-SCH = "Max T for SS heating Annual"
SS-VENT-CST = 5
SS-VENT-WND = 0.2
SS-VENT-TEMP = 0.2
SS-VENT-T-SCH = "Vent T Annual Schedule"
SS-VENT-SCH = "Sunspace Venting Schedule"
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (UVT) Heat Sch"
DESIGN-COOL-T = 75
BASEBOARD-CTRL = THERMOSTATIC
SIZING-OPTION = ADJUST-LOADS
SPACE = "EL1 North Perim Spc (G.N1)"
..
"EL1 North Perim Pl Zn (G.N6)" = ZONE
TYPE = UNCONDITIONED
DESIGN-HEAT-T = 67
DESIGN-COOL-T = 75
SIZING-OPTION = ADJUST-LOADS
SPACE = "EL1 North Perim Plnm (G.N6)"
Following is the error message
***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Pl Zn (G.N6) on 2/10 hr 11 (InitialFlg = 0)
SUNSPACE INTERIOR-WALL calculations produced bad values:
CSSVEC (convection) = 0. CSSVEC (conduction) = 7294864.
This would cause a 262. degree ZONE temperature change. Values are being ignored.
Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.
***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Zn (T.N11) on 2/10 hr 11 (InitialFlg = 0)
SUNSPACE INTERIOR-WALL calculations produced bad values:
CSSVEC (convection) = 0. CSSVEC (conduction) = 176604512.
This would cause a 6794. degree ZONE temperature change. Values are being ignored.
Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.
Any ideas as to where I went wrong?
- Christopher Ercoli