[Equest-users] Utility Meters and SubMeters in eQuest
Nick Caton
ncaton at smithboucher.com
Mon Jul 18 06:18:19 PDT 2011
Hi Seun - I'm sharing my response for others' benefit to understand how sub-meters are documented, I hope you don't mind!
Here are some select excerpts for illustration from your project:
>From BEPU:
TASK MISC SPACE SPACE HEAT PUMPS VENT REFRIG HT PUMP DOMEST EXT
LIGHTS LIGHTS EQUIP HEATING COOLING REJECT & AUX FANS DISPLAY SUPPLEM HOT WTR USAGE TOTAL
------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- --------
EM1 ELECTRICITY
KWH 86385. 0. 167249. 37739. 57318. 0. 15880. 71310. 0. 0. 26146. 5761. 467786.
>From PS-B:
JAN FEB MAR APR MAY JUN JUL AUG SEP OCT NOV DEC TOTAL
------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- --------
EM1 ELECTRICITY
KWH 40806. 38821. 39184. 39124. 33028. 37465. 40334. 42471. 41722. 37863. 35728. 41242. 467786.
MAX KW 130.3 129.7 143.6 147.2 160.4 144.7 145.1 193.5 179.5 162.2 150.2 129.3 193.5
DAY/HR 16/11 18/11 16/13 17/13 8/13 22/15 22/17 17/13 22/13 13/12 2/13 4/11 8/17
ELEV ELECTRICITY
KWH 2653. 2495. 2868. 2868. 2653. 2868. 2868. 2777. 2744. 2777. 2495. 2868. 32934.
MAX KW 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4 15.4
DAY/HR 2/ 9 2/ 9 2/ 9 1/ 9 1/ 9 1/ 9 1/ 9 3/ 9 1/ 9 1/ 9 2/ 9 1/ 9 1/ 2
>From PS-E, "all electric meters:"
TASK MISC SPACE SPACE HEAT PUMPS VENT REFRIG HT PUMP DOMEST EXT
LIGHTS LIGHTS EQUIP HEATING COOLING REJECT & AUX FANS DISPLAY SUPPLEM HOT WTR USAGE TOTAL
------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- ------- --------
KWH 86385. 0. 167249. 37739. 57318. 0. 15880. 71310. 0. 0. 26146. 5761. 467786.
MAX KW 28.689 0.000 68.391 17.727 67.449 0.000 5.817 25.761 0.000 0.000 5.208 1.315 193.501
MON/DY 1/ 2 0/ 0 1/ 8 2/ 4 8/17 0/ 0 8/17 8/17 0/ 0 0/ 0 1/ 2 1/ 1 8/17
PEAK ENDUSE 21.709 0.000 68.391 0.000 66.883 0.000 5.817 25.493 0.000 0.000 5.208 0.000
PEAK PCT 11.2 0.0 35.3 0.0 34.6 0.0 3.0 13.2 0.0 0.0 2.7 0.0
This all looks pretty normal to me! Page 127/160 of the "Help à Tutorials and Reference à Detailed Simulation Reports Summary.pdf" explains the BEPU report only shows one row for each utility meter. Sub-meters should not show up on that report, if that's what you're getting at.
The totals shown for EM1 (467,786 kWh) are inclusive of your Elevator sub-meter. You can test this by zero-ing out your elevator energy and observing the EM1 totals lowering by approximately 32,934 kWh. In fact, the sum lowers slightly more than that quantity, presumably because electric components of other conditioning equipment serving adjoining spaces are no longer handling the residual heat from the elevator equipment.
Rest assured, nobody should be expecting your elevator sub-meter to show up explicitly on BEPU. Its energies are rolled into the EM1 total. If you need to document the separate metering, PS-B should suffice. If documenting the sub-metered energies distinct from EM1 for LEED or similar, remember to pull the sub-metered quantities from the inclusive totals for EM1.
I will add that this "inclusive" nature of reporting when you have sub-metering defined was not immediately apparent or intuitive for me when I first encountered it... but maybe that was just me =)!
Hope this helps,
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Seun Odukomaiya [mailto:SOdukomaiya at lacquis.com]
Sent: Sunday, July 17, 2011 3:49 PM
To: Nick Caton
Subject: RE: [Equest-users] Utility Meters and SubMeters in eQuest
Nick,
Thanks for your reply. I have followed your instructions and still cannot get the BEPU report to show the submetered electricity. I have attached my pd2 and inp files for your review if you have some time. I'm curious to see why my model is behaving differently. Thanks again for all your help!
Seun Odukomaiya, EIT, LEED AP | Mechanical Engineer | L'Acquis Consulting Engineers |(317) 706-2075 Ext. 255 | www.lacquis.com <http://www.laceindy.com/> | To transmit large files, please use: http://lacquis.leapfile.net <http://lacquis.leapfile.net/>
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Thursday, July 14, 2011 6:47 PM
To: Seun Odukomaiya; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Utility Meters and SubMeters in eQuest
Hi Seun,
Hmm... I checked a previous project with sub-metering and did not find the same discrepancy between BEPU totals and the other reports... EM1's figures appear inclusive (not exclusive) of the sub-metered energies on PS-B. I could see that being unintuitive the way it's presented, and perhaps that's the root of the issue here?
PS-E and PS-F take the PS-B report further - one of those should show the sum totals for "all electric meters," broken out by energy end-use. That would seem a good place to start, to ensure all your sub-metered loads are being modeled and are accounted for. I am seeing BEPU totals that match, so if you see a mis-match it may be a sign that the sub-meters aren't correctly assigned to the utility meter (EM1)?
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Seun Odukomaiya
Sent: Thursday, July 14, 2011 2:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Utility Meters and SubMeters in eQuest
Hi guys,
In an effort to break out the electric consumption for the elevators in my building, I assigned that load to a submeter which I then assigned to the main utility meter EM1. This seems to have worked because I can see both meters and their respective consumptions in the PS-B report. Additionally, the ES-D report shows me that the total electric consumption for the building is being accounted for and billed according to my input utility rate. This is all fine and well.
When I look at the BEPU report, however, it only reports the energy consumption of the main utility meter, while ignoring the added consumption from the submetered elevator meter. Since my elevator meter is a submeter to the main electric meter EM1, shouldn't the BEPU report for EM1 show the total consumption of both meters? How do I get the BEPU report to show the total electric consumption? Thanks in advance!
Seun Odukomaiya, EIT, LEED AP | Mechanical Engineer | L'Acquis Consulting Engineers |(317) 706-2075 Ext. 255 | www.lacquis.com <http://www.laceindy.com/> | To transmit large files, please use: http://lacquis.leapfile.net <http://lacquis.leapfile.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110718/fd3c2555/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110718/fd3c2555/attachment-0002.jpeg>
More information about the Equest-users
mailing list