Did you try increasing the heating capacity of the central heating
coil or is is self-sizing. Are there under heated hours in the zones?
You note the warning is that the "system" may have insufficient
heating capacity. That doesn't sound like a zone problem so reheat
delta-t and zone entering max supply T likely are not the
problem. Hot Deck Max Leaving Temp. only applies to dual duct or
multi-zone systems (systems with 2 "decks"), not to single duct
systems like VAVS.
At 03:13 AM 22/07/2011, DongEun Kim wrote:
>Hi eQuesters!
>
>Can anyone help me here?
>
>I installed main heating coil as well as reheat coil with delta T=30.
>
>Heating capacity and cfm is not defined so that they will be auto-sized.
>
>And, I keep having this warning saying that the system "might have
>insufficient heating capability."
>
>I increased "Zone Entering Max Supply Temp", "Hot Deck Max Leaving
>Temp." But, the problem stays.
>
>
>How do I increase the heating capability?
>Thank you !!
>
>DE
>
>
>
>