[Equest-users] Default Values
Nick Caton
ncaton at smithboucher.com
Wed Jul 27 16:02:41 PDT 2011
To point #1:
I can't really provide a complete answer, but I can share some knowledge
to help shape the question perhaps...
Building Type (i.e. "Office") and certain energy standards are
selectable in detailed by clicking on the project line at the top of any
component tree.
These do affect the defaults of some inputs, similar to how the
type/jurisdiction options affect some wizards defaults. Not everything
has a default, and not everything that has a default has any bearing on
the building type/jurisdiction. You can begin to get a better picture
of where the default is coming from, if anywhere, by right clicking an
input field and selecting "view default/range."
The default for some inputs will be the input for something referenced
higher up the component tree (i.e. wall height of a space defaults to
the flr-to-clg height of the parent shell). The default for any linked
component is of course the linked object. Some inputs can reference
libraries (i.e. windows, constructions), and those selections if used
will in some cases set "defaults" for other entries.
If what you're getting at is the desire to revise/define different
defaults, then you should explore "edit/view user default..." in the
same context dialog.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Robby
Oylear
Sent: Wednesday, July 27, 2011 4:49 PM
To: Bradley Donohue
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Default Values
Bradley,
1. Don't know the answer to this question. What value are you trying to
restore to default in detailed mode? Jurisdiction has no effect on the
actual input of the detailed file as far as I know. Building type
should also not have any direct impact on the model, it just helps the
wizard to determine default values for other items (HVAC systems types
available, lighting and plug load values).
2. The infiltration values from the wizard are converted to a CFM/SF
value in detailed mode. There is no constant factor. Say you enter
0.05 CFM/SF of wall area in the wizard and for a particular space this
equates to 50 CFM. The wizard converts this to a CFM/SF number by
dividing the calculated infiltration value from your inputs (50 CFM) by
the floor area of the space.
Hope this helps,
Robby Oylear, LEED(r) AP BD+C
Mechanical Project Engineer
Energy Analyst
D 206-788-4571 | C 206-354-2721
www.rushingco.com <http://www.rushingco.com/>
On Wed, Jul 27, 2011 at 2:03 PM, Bradley Donohue <brad.donohue at me.com>
wrote:
Hello,
I have two questions,
1. I was wondering where an equest model takes its default values from
if it was completely constructed in the detailed mode. Because the
modeler does not choose a building type or jurisdiction I am not sure
where the values come from if you restore to default.
2. When changing from the wizard to detailed edit the infiltration
values change to a by floor area number. What variable or factor does
equest apply when making this automatic change?
Thanks,
Brad
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110727/3f4f2379/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110727/3f4f2379/attachment-0002.jpeg>
More information about the Equest-users
mailing list