[Equest-users] Actual vs model- utiltiys
John Aulbach
jra_sac at yahoo.com
Wed Jun 29 11:12:18 PDT 2011
Mike:
That spreadsheet came from me via an "Unimpeachable source". You run eQuest,
extract the "cut and paste" from the .CSV file created in .sim file and compare
it to actual utility data. You NEVER can input utility data directly into eQuest
and expect it to disseminate (sp?) electricity, for example, into lights, plug
lod, space cooling, etc.
BTW, the spreadsheet has an interesting feature in that you can put a multiplier
into the spreadsheet to see what elements in your model may need "tweaking" in
order to match your bills.
Unfortunately, I do not have a tool whereas you can input actual weather from
that year and modify the model to match the real weather (a competing program
DOES).
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: mike steadman <steadys at charter.net>
To: equest-users at lists.onebuilding.org
Sent: Wed, June 29, 2011 7:10:41 AM
Subject: [Equest-users] Actual vs model- utiltiys
Ok,
here is my stupid question-I deleted my equest box with some great answers
Some one sent me this wonderful spreadsheet about utilitys-thank you
yet I am cloudy on what the answer really means for inputting actual utilty use
into my model.
Is that even done with equest and if so, where in the process can you do it,
Schematic wizard.? DD wizard?
I see rates for block, demand , yet nothing for inputting the exact amount of
therms or KWH in each month with usage numbers, I have built my model and saved
in DD mode so editing the utilty use from the component tree seems to not work?
My memory with this attached spreadsheet - I would run my building simulation
and save to a sheet like this and then revise to current usage and somehow
upload back into my model. WoW.!!
Can anybody help with that process
Thanks in advance
Mike S
Energy Manager
ABI Mechanical
Traverse City Michigan 49685
231-943-4114 ext 250
msteadman at abimechanical.com