[Equest-users] No heating in winter
Boxer, Eric
eboxer at pathfinder-ea.com
Tue May 31 13:08:42 PDT 2011
Greetings, Vipin;
I opened your GSHP project here, and ran it with a weather file for
Rochester, NY, USA. The winters are quite cold here, and as I thought,
it shows some heating in a consistent fashion between November and
April. However, as you can see below, miscellaneous equipment energy far
outweighs this. This is very unusual. This means there are plug loads
within your building which are also heating the building. In fact, you
have 6.9 W/sq. ft. entered as the load. I would suggest reducing this
amount to about 1.2 w/sf for a typical office.
Cheers,
Eric
From: Vipin Sharma [mailto:sharma_vipin138 at yahoo.com]
Sent: Saturday, May 28, 2011 1:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] No heating in winter
Hi..................
Greetings
I have applied GSHP in my project in composite
climate in India but it is not showing heating in winter. I need heating
load in winter from Nov. to Dec. .Can anyone
resolve this problem.
Help will be appreciated.
Thanks in advance.
vipin sharma
Energy Engg.
student
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110531/6afacdd7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 25154 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110531/6afacdd7/attachment-0002.jpeg>
More information about the Equest-users
mailing list