[Equest-users] No heating in winter
Nick Caton
ncaton at smithboucher.com
Tue May 31 15:00:24 PDT 2011
Eric, thanks for the pictorial!
I'd agree with Eric's assessment and offer extra food for
thought/context: I believe 90.1-2007 users manual suggests 0.75 W/SF as
typical for office building plug loads.
Further qualitative perspective: Picture how hot a 60W incandescent
A-lamp gets... Now imagine 60W light bulbs on a 10ft grid all turned
on... that (6W/SF) is a significant amount of heat!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Boxer,
Eric
Sent: Tuesday, May 31, 2011 3:09 PM
To: sharma_vipin138 at yahoo.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] No heating in winter
Greetings, Vipin;
I opened your GSHP project here, and ran it with a weather file for
Rochester, NY, USA. The winters are quite cold here, and as I thought,
it shows some heating in a consistent fashion between November and
April. However, as you can see below, miscellaneous equipment energy far
outweighs this. This is very unusual. This means there are plug loads
within your building which are also heating the building. In fact, you
have 6.9 W/sq. ft. entered as the load. I would suggest reducing this
amount to about 1.2 w/sf for a typical office.
Cheers,
Eric
From: Vipin Sharma [mailto:sharma_vipin138 at yahoo.com]
Sent: Saturday, May 28, 2011 1:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] No heating in winter
Hi..................
Greetings
I have applied GSHP in my project in composite
climate in India but it is not showing heating in winter. I need heating
load in winter from Nov. to Dec. .Can anyone
resolve this problem.
Help will be appreciated.
Thanks in advance.
vipin sharma
Energy Engg.
student
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110531/fafbd60e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110531/fafbd60e/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 25154 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110531/fafbd60e/attachment-0005.jpeg>
More information about the Equest-users
mailing list