[Equest-users] Supporting to review detail project
    Nick Caton 
    ncaton at smithboucher.com
       
    Mon Nov  7 15:59:20 PST 2011
    
    
  
Hi Thu,
 
This looks like a good opportunity to share some things for everyone to
consider when encountering unmet hours... I'd encourage others to read
along!
 
CAUTION:  the files you sent include a 0kB INP file... if it isn't too
late, you should save a copy in a new location if you still have your
project open!
 
That said, the files you did send included a SIM report file from which
I can suggest a few things.  
 
Scrolling through the space temperature summary (SS-O), you have some
very different distributions of binned hours between the zones... many
are floating higher (into the 85+ range) for much of the year...  SS-R
suggests the problem is not isolated to any particular zone/system (I
would normally verify this in my own models using the airside summary
tab after a simulation).
 
A few things catch my eye: 
*         You have a fan schedule for at least one system with zeroes
entered through the work day... I can tell you are trying to define
"residential" and "non-residential" scheduling for different spaces
under the same project... but be very careful you aren't mis-applying
any such system & load scheduling in this sense or you'll have a lot of
cooling that will not be served because your fans are simply off.  The
inverse applies for those systems whose fans are noted "off" in the
evening.  A review of your night-setback inputs may worth your time as
well.
*         As an extension of the first bullet:  Looks like you are
trying to define a cooling setback temperature of 104 degrees using your
zone cooling schedule... check whether that really makes sense.  A
~30-degree differential is going to be tough for any non-oversized
system to catch up with if the building should float far beyond the set
point.
*         Another reason your systems might have trouble keeping up:
this is not necessarily "wrong," but fractional schedules for things
like plug loads and occupancy ordinarily lie in-between 0 and 100% for
an energy model.  Case in point:  100% misc equipment loads and
occupancy for all occupied hours is likely exacerbating the unmet
cooling hour situation (consider these items as an internal heat load),
and may simultaneously be a reason  you have zero unmet heating hours to
consider at the moment although the reports are cautioning you
extensively on the topic of heating capacities...  
 
Not an exhaustive review, but may help you identify a few stumbling
blocks.  If you wish to re-engage the list with your files in the
future, I'd advise including your weather file and ensuring your INP
file is not empty.  
 
Best of luck!
 
~Nick
 
 
 
NICK CATON, P.E.
SENIOR ENGINEER
 
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Thu
Nguyen - Indochine Engineering
Sent: Sunday, November 06, 2011 10:44 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Supporting to review detail project
 
Dear all users, 
 
I'm modeling a project like the attached, with included: office for
staff, dormitory for expert, canteen kitchen for expert and worker. 
 
I'm already fix the schedule for each system following as their properly
schedule. But the unmet hour result still high, out of allowance. 
 
Please would you have a favor to review this modeling and instruct for
me, the detail reason make this wrong. 
 
Thanks so much and hope to see your feedback soon.
 
Regards,
Thu Nguyen
 
Indochine Engineering Vietnam Ltd
Unit 5, 8th Floor, A&B Tower, 76 Le Lai Street
District 1, HCMC, Vietnam
 
Mobile:  +84 (0) 985 277 099 
Tel:  +84 (8) 6290 9400 Ext 300
Fax: +84 (8) 6290 9406
 
Web: www.indoeng.com <http://www.indoeng.com/> 
Skype
<mailto:tien at indoeng.com?subject=Feedback%20on%20ICE%20Quality%20System>
: huongthu.nguyen
 
Annex:
Ho Chi Minh                            Ha Noi
Da Nang
5F FAFILM Bldg                     Suite 429, 4F, Regus Press Club
6F Indochina Riverside Tower Bldg
6 Thai Van Lung St                  59 Ly Thai To St
74 Bach Dang St
District 1, HCMC, Vietnam      Hoan Kiem District, Ha Noi, Vietnam
Hai Chau District, Da Nang, Vietnam
Tel:  +84 (8) 6290 9400           Tel:  +84 (4) 3936 7926
Tel:  +84 (511) 222 1200
Fax: +84 (8) 6290 9406            Fax: +84 (4) 3936 8069
Fax: +84 (511) 222 1201
 
Email us for any feedback on Indochine Engineering
<blocked::mailto:carl at indoeng.com?subject=Feedback%20on%20ICE%20Quality%
20System> 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111107/bac53521/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111107/bac53521/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list