[Equest-users] Review Comment - Equipment capacities for the Proposed
Omar Katanani
omar at ecoconsulting.net
Thu Oct 6 01:09:07 PDT 2011
Dear all,
I have received the following LEED design review:
"Mechanical drawings with equipment schedules (M-04, M-05, and M-06)
with the heating and cooling pumps, boiler, chiller, and cooling tower
schedules have been provided. However, the scheduled flows and
capacities are inconsistent with those reported in the Table 1.4.3 in
the spreadsheet.
Please revise the Proposed model to reflect the design conditions
(including all capacities, flows, controls, and setpoints), revise the
form and spreadsheet as required to reflect any changes, and provide
reports or screen captures to confirm the changes made."
My impression was that we don't have to enter the capacities / flows (as
per the Mechanical design) in eQUEST, as the program automatically
calculates/sizes these.
The reviewer noticed an inconsistency between Table 1.4.3 (whereby I
filled in the equipment capacities & loop flows from the eQUEST
Simulation Output reports) and the Mechanical schedules.
Shall I rerun my simulations with whatever capacities/schedules provided
by the Mechanical Engineers?
Thanks,
Omar
Please note that EcoConsulting is holding a new series of eco-seminars
on Green Building & LEED GA Training in November.
More information available at:
http://ecoconsulting.net/www/Seminar_Series_Lebanon_Nov11.htm
<http://ecoconsulting.net/www/Seminar_Series_Lebanon_Nov11.htm>
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111006/5318894f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111006/5318894f/attachment.jpeg>
More information about the Equest-users
mailing list