[Equest-users] Ground Water/chilled water loop error(s)
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Tue Oct 18 17:55:31 PDT 2011
Travis - took a little more time and read the whole thing.
Why not put the offending chiller (and associated circulation pump) on a separate utility meter and just subtract that meter from your total usage as a post-processing exercise?
I'm not sure whether or not eQUEST can explicitly model what you're trying to do.
Aaron Dahlstrom , PE, LEED® AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: Dave Bastow [mailto:dbastow at mcclure-engineering.com]
Sent: Tuesday, October 18, 2011 5:39 PM
To: 'Travis Miller'; Dahlstrom, Aaron; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Ground Water/chilled water loop error(s)
Travis,
If nothing else you can model it as a regular chiller with an open cooling tower and just use KW/efficiency factors & curves for the various components so that it equals what you would get from energy used by your well pumps or what have you. Also, using temperatures that relate to your well water temperatures for the chilled water temperatures. I did this once, modeling an existing large office building that was cooled by well water, that varied from 50 degrees F. in winter to 60 degrees F. in the late summer. Once I got all the inputs and curves and all set up correctly then it modeled very closely to what the actual energy use had been from all of our historical recorded data.
David A. Bastow
McClure Engineering, Inc.
507 Main Avenue West
Post Office Box 1404
Twin Falls, Idaho 83303-1404
PH. (208) 734-9015
FAX (208) 734-9016
Cell (208) 308-1152
E-Mail: dbastow at mcclure-engineering.com<mailto:dbastow at mcclure-engineering.com>
Web Site: www.mcclure-engineering.com<http://www.mcclure-engineering.com/>
From: Travis Miller [mailto:tmiller at dcengineering.net]<mailto:[mailto:tmiller at dcengineering.net]>
Sent: Tuesday, October 18, 2011 9:28 AM
To: Dahlstrom, Aaron; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Ground Water/chilled water loop error(s)
Thanks Aaron - I did that and now the error reads:
[cid:image001.png at 01CC8DD8.461363F0]
So I went and gave the chilled water loop the same process load, but that did not fix the problem. Below is a screenshot on how the loops are tied together. Ignore the heat pump loop - that is for a different system in the same building. Any other thoughts would be appreciated. Thanks
[cid:image002.png at 01CC8DD8.461363F0]
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]<mailto:[mailto:ADahlstrom at in-posse.com]>
Sent: Monday, October 17, 2011 5:18 PM
To: Travis Miller; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Ground Water/chilled water loop error(s)
Travis - sometimes this error can be addressed by putting a nominal process load on the offending loop - say 0.000001 Mbtu/hr, with a minimal schedule.
There may be a more comprehensive or elegant solution, but this might just get you going.
AD
Aaron Dahlstrom , PE, LEED® AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org]<mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> On Behalf Of Travis Miller
Sent: Monday, October 17, 2011 5:45 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Ground Water/chilled water loop error(s)
Hello all:
I have a system that is using well water direct to the cooling coils (no heat exchanger to protect the cooling coils) at multiple air handlers in the building. I set it up with the condenser water loop tied to a ground water heat exchanger. This condenser loop then is tied to another heat exchanger on the chilled water loop to the coils. This approach has given me an error on the condenser water loop that it has no design flow. I have been playing with the primary/secondary loop designations, even putting some made up flow values into the loops/pumps etc. but have had no luck. Any ideas?
I would like to eliminate heat exchangers all together and just model the 50° well water directly into the chilled water loop - any advice on how to do this? I already changed the effectiveness of the heat exchanger to 1.0.
Thanks
Travis Miller, PE
DC Engineering
123 W. Spruce St.
Missoula, MT 59802
P: (406)829-8828x209
F: (406)829-8829
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/3dd206d2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 26778 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/3dd206d2/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 20500 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/3dd206d2/attachment-0005.png>
More information about the Equest-users
mailing list