[Equest-users] wwr calculation
    deepika khowal 
    deepika.khowal at gmail.com
       
    Wed Oct 19 14:15:01 PDT 2011
    
    
  
I agree with James .
if its unconditioned space, we should not claim the window area . that way
we can have higher WWR for rest of conditioned spaces.
On Wed, Oct 19, 2011 at 1:56 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
> I don't think I agree with this advice****
>
> ** **
>
> Under ASHRAE 90.1-2007, Section 5.2.1, part of the requirements for the
> PRESCRIPTIVE method requires that "the vertical fenestration area does not
> exceed 40% of the gross wall area for each *space-conditioning category*".
> ****
>
> ** **
>
> The definition for "space conditioning category" simply says:****
>
> ** **
>
>                 non-residential conditioned space,****
>
>                 residential conditioned space, and****
>
>                 nonresidential and residential semiheated space****
>
> ** **
>
> It doesn't list unconditioned space.  Now I know this info is listed in the
> prescriptive requirements, but if it was my model, and I had a garage that
> had 100% window area, there is no way I would count that towards the gross
> WWR, particularly if I was applying for LEED, and these inconsequential
> windows pushed my WWR above 40% and thus penalized my proposed building.  In
> fact, I might not even model the windows, unless I felt they were going to
> superheat the garage and start impacting adjacent space cooling loads.****
>
> ** **
>
> Just my opinion...****
>
> ** **
>
> *GHT Limited
> **James Hansen, P.E., LEED AP*
> Senior Associate
> 1010 N. Glebe Road, Suite 200
> Arlington, VA  22201-4749
> 703-243-1200 (office)****
>
> 703-338-5754 (cell)
> 703-276-1376 (fax)****
>
> www.ghtltd.com****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *PKConsulting
> *Sent:* Wednesday, October 19, 2011 4:04 PM
> *To:* deepika khowal
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] wwr calculation****
>
> ** **
>
> It doesn't change for unconditioned or conditioned.  It is only a function
> of gross wall area (ft2) and window area (ft2).   Don't think too hard about
> this.  You are looking for a needle in the wrong haystack.   This one is
> straight forward with no tricks...****
>
> ** **
>
> WWR is for whole bldg not space by space.****
>
>
> Pashalu****
>
>
> On Oct 19, 2011, at 12:20 PM, deepika khowal <deepika.khowal at gmail.com>
> wrote:****
>
> Thanks Pasha****
>
> ** **
>
> yes , i have been using LV-d report.****
>
> ** **
>
> Am confused how it work for an unconditioned space.****
>
> Thanks****
>
> On Wed, Oct 19, 2011 at 11:01 AM, PKConsulting <
> pasha.pkconsulting at gmail.com> wrote:****
>
> It should be the gross wall area for everything above ground.  Use the lv-d
> report to find the numbers to calculate the overall WWR for your entire
> bldg.   There is a summary page at the end of the lv-d report.  Look for the
> line called-'all walls'.  You can use those numbers to calc WWR percentage.
>
> Pashalu****
>
>
> On Oct 19, 2011, at 11:39 AM, deepika khowal <deepika.khowal at gmail.com>
> wrote:
>
> > Hi all
> >
> > I have a question about calculating WWR.
> > for example, if the south wall area is 700sf and total window area is
> 70sf then the WWR should be 10%.
> > but if 50% of south wall is part of a garage and is unconditioned, then
> in calculating WWR , should I include only the wall area for conditioned
> space or it should include complete facade?
> > Thanks
> >
> > Deepika
> >
> >
> >
> >****
>
> > <image.png>
> > _______________________________________________
> > Equest-users mailing list
> > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> > To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
> ** **
>
> ------------------------------
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee.  It is the
> property of GHT Limited.  Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful.  If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments.  Thank you.
>
>  <#1331df8e63c7b347_>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111019/1c5e97b3/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list