[Equest-users] Unoccupied fan turning on
Arpan Bakshi
arpanbakshi at gmail.com
Thu Aug 9 10:03:14 PDT 2012
I would check heating and cooling schedules, and more importantly, make sure schedules are actually assigned! It is easy to make a schedule thinking it will automatically be attached; not true.
Arpan Bakshi, BD+C, PQP
T (646) 704-2880
YR&G
www.yrgxyz.com
...
On Aug 9, 2012, at 12:54, Adam Rustige <ARustige at fdh-inc.com> wrote:
> Hello,
>
> First time posting a question. The fan on multiple AHU’s are turning on during unoccupied periods when the space is above the set point. The heating and cooling stays off when the fan comes on, so I think having the fan on is causing my issue with unmet hours. I have checked AHU’s that have 0 unmet hours and the fan is following the schedule. All the AHU’s have the same schedule. Has anyone seen this issue?
>
>
>
> Thanks, Adam
>
>
>
> Adam Rustige
>