You have two options -
1. Turn the night-cycle parameter off - so they won't come on during the
unoccupied times, even if the temp is beyond the setback. Alternatively
increase the setback.
2. Allow the cooling/heating to be available all the time. Or have
economizer for night time cooling - might help if it is a cool climate -
won't help for summer weekends.

Depends on what the actual configuration is.
-Rohini

On Thu, Aug 9, 2012 at 11:54 AM, Adam Rustige <ARustige at fdh-inc.com> wrote:

> Hello,****
>
>           First time posting a question.  The fan on multiple AHU’s are
> turning on during unoccupied periods when the space is above the set
> point.  The heating and cooling stays off when the fan comes on, so I think
> having the fan on is causing my issue with unmet hours.  I have checked
> AHU’s that have 0 unmet hours and the fan is following the schedule.  All
> the AHU’s have the same schedule.  Has anyone seen this issue?****
>
> ** **
>
> Thanks, Adam****
>
> ** **
>
> Adam Rustige****
>
> Energy Analyst
>
> FDH, Inc.
> 222 S. Central Ave, Suite 1110
> St. Louis, MO 63105
> Office: 314.773.4000 · Mobile: 314.699.8948
> Fax: 314.773.4002 · Email: arustige at fdh-inc.com
>
> www.fdh-inc.com <http://www.fdh-inc.com>
> Raleigh · St. Louis · Baton Rouge****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120809/3d4c7d61/attachment-0002.htm>


More information about the Equest-users mailing list