I would look into the enthalpy wheels more. I usually zero out the kW/cfm
on the wheels if the fan energy is already accounted for elsewhere, but
still leave a 0.0001 dP accross the wheel. Also, try leaving the CFMs at
default in the supply and exhaust inputs for the wheel. Occasionally these
cause issues because the fan is trying to get more airflow from the fan.
Hope that helps,
Rob H
On Wed, Dec 12, 2012 at 10:03 AM, Joe Bliss <JBliss at b2qassociates.com>wrote:
> Hello all,****
>
> ** **
>
> Does anyone know exactly what’s included in the “Total SYSTEM/ZONE fan
> (supply, return, exhaust) elec consump (kw)” value in hourly reports? I am
> having an issue with my model where I have unexpectedly high fan energy use
> and when I trend the aforementioned point along with the supply and return
> fan power, the total system/zone fan kW is much greater than the sum of the
> supply and return fan kW. In some cases 10 times greater. I’m using PVAV
> system type with enthalpy wheels. I’ve zeroed out the dP across the wheel
> because I have a given fan capacity. No fan-powered boxes in the zones. No
> exhaust fans in the zones. I’m stuck trying to determine where the extra
> fan energy is coming from.****
>
> ** **
>
> Any help would be greatly appreciated.****
>
> ** **
>
> Thanks,****
>
> Joe****
>
> ** **
>
> *Joe Bliss*
>
> Designer****
>
> *B2Q Associates, Inc.*
>
> 146 Main Street #2****
>
> North Andover, MA 01845****
>
> Office: 978.208.0609 x210****
>
> Mobile: 774.277.0662****
>
> Fax: 978.719.6339****
>
> www.b2qassociates.com****
>
> ** **
>
> The contents of this e-mail and any attachments are confidential and the
> property of the B2Q Associates, Inc. The e-mail contents are only to be
> used by the intended recipient of the e-mail. If you are not the intended
> recipient then use, disclosure, copying, distribution or reliance on the
> e-mail is prohibited. All professional advice from us should be obtained in
> writing (not e-mail).****
>
> ** **
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121212/ae4281c4/attachment-0002.htm>
More information about the Equest-users
mailing list