[Equest-users] PVAV Fan Energy
Bishop, Bill
bbishop at pathfinder-ea.com
Wed Dec 12 07:52:58 PST 2012
Fan energy attributable to the enthalpy wheels will appear in the ERV Energy Recovery Summary reports. It is also included (but not broken out) in the SS-H, SS-L and SS-M reports, except for the bottom portion of SS-L where the supply and return fans are broken out.
Hint: For the SS-L and SS-M reports,
Total fan electric (FE) energy = FE during heating + FE during cooling + FE during floating - FE during heat & cool
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Wednesday, December 12, 2012 10:17 AM
To: Joe Bliss
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] PVAV Fan Energy
I would look into the enthalpy wheels more. I usually zero out the kW/cfm on the wheels if the fan energy is already accounted for elsewhere, but still leave a 0.0001 dP accross the wheel. Also, try leaving the CFMs at default in the supply and exhaust inputs for the wheel. Occasionally these cause issues because the fan is trying to get more airflow from the fan.
Hope that helps,
Rob H
On Wed, Dec 12, 2012 at 10:03 AM, Joe Bliss <JBliss at b2qassociates.com<mailto:JBliss at b2qassociates.com>> wrote:
Hello all,
Does anyone know exactly what's included in the "Total SYSTEM/ZONE fan (supply, return, exhaust) elec consump (kw)" value in hourly reports? I am having an issue with my model where I have unexpectedly high fan energy use and when I trend the aforementioned point along with the supply and return fan power, the total system/zone fan kW is much greater than the sum of the supply and return fan kW. In some cases 10 times greater. I'm using PVAV system type with enthalpy wheels. I've zeroed out the dP across the wheel because I have a given fan capacity. No fan-powered boxes in the zones. No exhaust fans in the zones. I'm stuck trying to determine where the extra fan energy is coming from.
Any help would be greatly appreciated.
Thanks,
Joe
Joe Bliss
Designer
B2Q Associates, Inc.
146 Main Street #2
North Andover, MA 01845
Office: 978.208.0609 x210<tel:978.208.0609%20x210>
Mobile: 774.277.0662<tel:774.277.0662>
Fax: 978.719.6339<tel:978.719.6339>
www.b2qassociates.com<http://www.b2qassociates.com/>
The contents of this e-mail and any attachments are confidential and the property of the B2Q Associates, Inc. The e-mail contents are only to be used by the intended recipient of the e-mail. If you are not the intended recipient then use, disclosure, copying, distribution or reliance on the e-mail is prohibited. All professional advice from us should be obtained in writing (not e-mail).
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121212/9407ecf6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121212/9407ecf6/attachment-0002.jpg>
More information about the Equest-users
mailing list