Window6 can model complex glazing like Venetian blinds between the glass panes.
At 08:51 PM 22/12/2012, Peter Baumstark wrote:
>Ok. . . I have a situation where I'm modeling a facility relative
>to ASHRAE 90.1 baseline. The customer is using dual pane, low-e
>windows, with integrated venetian blinds between the two panes of
>glass. One pane is low-e and the other is clear. Air gap between
>the two (not Argon or anything like that).
>
>I use the LBNL Windows tool, with blinds set at 45 deg, and the
>blinds increase the window assembly U value and SHGC significantly.
>
>So for performance relative to 90.1, would it be acceptable to
>simply utilize the U & SHGC from with Windows tool? Are there any
>restrictions on the angle of the blinds, or whether the angle should
>be different for winter vs summer?
>
>I'd appreciate any guidance on how to best model this scenario.
>
>Thank you,
>Pete Baumstark
>San Jose, CA
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121226/3bd79fea/attachment-0002.htm>
More information about the Equest-users
mailing list