[Equest-users] wall composition and U value
Nick Caton
ncaton at smithboucher.com
Wed Feb 29 15:09:55 PST 2012
Interesting case: I've modeled exactly as you've described for a very unique existing case where the windows were spray-painted opaque from the inside...
(PS: spray-paint does *not* hold up well over time on exposed glass - file that away as a pretty bad idea)!
Vikram is right: your approximation including windows would correctly approximate the non-solar heat transfer loads but will fall short when it comes to solar loads, which are usually a big enough deal to warrant actually specifying the windows. Averaging the non-window constructions is often a very acceptable time-saving measure, especially when the constructions are largely similar. I would think twice before averaging together constructions with very different properties.
A tip: if you are going to go through the effort of defining your uvalues separately for each wall construction, it may be worth noting eQuest will tally the net u-value for each construction automatically if you use the layers approach, much like other load calculation software. I find that as easy as any other method, and you get a weighted construction as icing on the cake ;).
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Wednesday, February 29, 2012 1:25 PM
To: tanyer at metu.edu.tr; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] wall composition and U value
You need to separate out the windows - only model opaque elements as walls. Model the windows as windows.
Otherwise - it should be fine to model the wall as a homogenous average of the multiple layers - you should be able to do a weighted average calc.
Do you have insulation? Does it run continuous over everything?
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com
Perkins+Will. Ideas + buildings that honor the broader goals of society
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tanyer at metu.edu.tr
Sent: Wednesday, February 29, 2012 8:57 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] wall composition and U value
Dear all,
I am trying to find the U value of a wall which is composed of concrete beams and colums (20%) masonry (60%) and glazing (20%).
I know the U values of the components and I would like to calculate the average U value for this wall since it is a single entity in eQuest.
Do I need to include the area of the glazing when calculating the total U value?
0.2 x Ucnct + 0.6 x Umsry + 0.2 x Uglzg
OR, do I have to extrapolate the concrete and the masonry parts as if covering the glazing part?
0.25 x Ucnct + 0.75 x Umsry
As you know we also define the glazing U value later seperately.
Thanks
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list