[Equest-users] LEED Compliance Analysis error
RIAD ABED
riad_abed at hotmail.com
Fri Jan 6 21:34:52 PST 2012
Dear Tanyer
The Solution to your problem is :
in detailled Mode Of " Project & Site" Tab, (U will find in the Top Of Window Bard Command), click it, then at the Left (In Component Tree) , u will find Icon "Site Plan". click it & u should then fill :
1- Climate Zone Number (according to Table B-3 & B-4 of ashrae 90.1.2007 for your location)
2- Climate Zone letter (according to Table B-3 & B-4 of ashrae 90.1.2007 for your location)
3- Latitude (of your Location)
4- longitude (of your location)
Note : u should be in Detailled Data Edit Mode , and when u will fill the above requirement u should, maybe when u want to enter the value , right click then Edit/View User Default The in the space "User-Defined Default Value" put yout value that u want to enter it.........
Good Luck
Best regards,
Eng. Riad el Abed
Chief MEP & Project Manager
PQP & Energy Modeling Expert
Mob : 961 70 643977
Email : riad_abed at hotmail.com
Web : www.riadabed.com
Forum : www.riadabed.com/vb
__________________________________________________________________________________________________________________________________________
Date: Fri, 6 Jan 2012 15:34:36 +0200
From: tanyer at metu.edu.tr
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Compliance Analysis error
Dear all,
I am trying to simulate the LEED compliance of an office building located in Europe and I have a couple of questions:
Can I provide the LEED compliance of a building which is located in Europe?
If I select my EU city and provide its weather data file I get the following error message: "Table Look-up failed:A901-0_Envelope(1,4): Look-up and default C-FFACTOR for slabs". I tried to define the FFactor for my underground slabs but not worked.
If I select, for example, Seattle weather file, I can get rid of this error message.
Does eQuest provide the necessary requirements (rotations, materials, etc) of the baseline design automatically?Many thanks in advance.
_______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120107/d9a4bba4/attachment-0002.htm>
More information about the Equest-users
mailing list