[Equest-users] Internal Wall Problems with Wizard
Nathan Miller
nathanm at rushingco.com
Tue Jul 10 10:59:56 PDT 2012
To further clarify, if you look at the walls you highlighted as “missing” in
Image 1 (when you select the smaller space), you will see that they appear
in Image 2, meaning as Robby indicated, they are a child component of the
larger space that surrounds the smaller space. You should be able to select
them and verify that the NEXT-TO field is properly entered.
Also, I thought that the space that gets “possession” of an interior wall
has something to do with the order that you draw them in the wizard, but it
has been a long time since I cared to check on that.
Nathan Miller, PE, LEED AP BD+C
Mechanical Engineer/Senior Energy Analyst
O 206-285-7100 | D 206-788-4577
<http://www.rushingco.com/> www.rushingco.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Robby
Oylear
Sent: Tuesday, July 10, 2012 10:47 AM
To: omoltay at mimtarch.com
Cc: eQUEST Users List
Subject: Re: [Equest-users] Internal Wall Problems with Wizard
Regarding the comment about not trusting eQUEST's snaps, I find it helps to
turn all snaps except "Polygon" off when defining zones. Thus the only way
it's snapping is directly onto an existing vertex. I use this every time
and don't have any issues with interior walls.
Omer-
I believe what you're experiencing is that when defined properly, eQUEST
only defines ONE interior wall. Since an interior wall is used to define a
relationship between two spaces, there is only need for one wall. The zone
that own's the wall is rather arbitrary, because either way they are linked
through the NEXT-TO command. If two walls are created by eQUEST, it's
likely that they'll both be ADIABATIC and this is a symptom of not defining
the wall geometry correctly. One wall per zone interface is what you should
be shooting for.
-Robby
On Tue, Jul 10, 2012 at 10:25 AM, Ömer Moltay <omoltay at mimtarch.com> wrote:
Hi Robby,
Thanks a lot. Learned something very important today.
Another problem that I am having with internal walls: There are internal
walls missing in some zones and I have no clue as to why. You will see these
in the attached images as thin lines. The walls are missing from the
selected zone (grayed), but the neighboring zone has walls in the same
place.
In 01.jpg, all three internal walls of the smaller zone are missing.
In 02.jpg, some internal walls are missing and some are not.
This floor has been recreated according to your advice with additional
vertices.
I think there is more to internal walls in Wizard that I do not know.
Best regards,
Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, CPMP, BREEAM Assessor
Mimta EcoYapi
Hekimsuyu Cad. 559. Sk.
No:39 34255 Küçükköy İstanbul
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.ekoyapi.net
www.mimtasolar.com
www.mimtarch.com
10.07.2012 18:52 tarihinde, Robby Oylear yazdı:
Omer,
The simplest way to ensure that eQUEST defines the NEXT-TO property
correctly is to make sure that each interior wall only interfaces with one
other interior wall.
In the situation you describe where you have an interior wall that is
adjacent to more than one zone, I would typically split that interior wall
into two or three walls by adding vertices at each of the intersections
between the zones and the interior wall that spans them.
Here's a sketch of what I'm describing:
Inline image 1
Hope that helps.
Robby Oylear, PE, LEED AP
Mechanical Engineer
Senior Energy Analyst
D 206-788-4571
<http://www.rushingco.com/> www.rushingco.com
On Tue, Jul 10, 2012 at 8:45 AM, Ömer Moltay <omoltay at mimtarch.com> wrote:
Dear All,
I have realized that while creating the model after Wizard entries, eQuest
will fail to determine the NEXT-TO property for interior walls that are
adjacent to more than one zone and all those interior walls will be defined
as ADIABATIC.
Also, I see that interior walls are missing from zones where another zone
has an ADIABATIC wall in the same place.
I see no way of having a model with all interior walls correctly defined
without fixing all these problems after the Wizard. Does everybody have the
same experience or am I missing something?
Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, CPMP, BREEAM Assessor
Mimta EcoYapi
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.ekoyapi.net
www.mimtasolar.com
www.mimtarch.com
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120710/22a4b003/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10321 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120710/22a4b003/attachment-0002.png>
More information about the Equest-users
mailing list