[Equest-users] Exterior Building Lighting Power Compliance (Non-Tradable Lighting Applications)
Robby Oylear
robbyoylear at gmail.com
Fri Jul 27 08:10:01 PDT 2012
Per ASHRAE 90.1-2007 section 9.4.5 you can only exceed the allowed exterior
lighting power allowance by 5% in order to be in compliance with this
section. Section 9.4.5 is a mandatory provision and thus you must comply
with it in order to satisfy the LEED EA Prerequisite 1.There are a number
of lighting applications that are exempt from the total power allowance as
outlined in the exceptions to section 9.4.5.
Robby Oylear, PE, LEED AP
*Mechanical Engineer*
*Senior Energy Analyst*
* *
*D* 206-788-4571
*www.rushingco.com* <http://www.rushingco.com/>
On Thu, Jul 26, 2012 at 1:59 PM, Caballero, Catalina
<ccaballero at jalrw.com>wrote:
> Hi, does anybody know if your installed exterior lighting for non-tradable
> applications (façade) consumption is bigger than allowed, you would not
> pass the credit? Is there some type of exemption to this?****
>
> ** **
>
> Regards,****
>
> ** **
>
> C.****
>
>
> ****
>