[Equest-users] Texas OPERATIONAL Ventilation Requirements - eQuest Related
John Aulbach
jra_sac at yahoo.com
Wed Jun 6 10:25:38 PDT 2012
Gang:
I am trying to find where in the Texas Health and Safety Code where is says you must OPERATE ventilation in a certain manner, not just design a system to provide such ventilation. Tells me if i can reduce or eliminate exhaust air during certain times of the day (eQuest EEM).
California Title-24, Subchapter 3, Section 121.c.1 specifically states:
1. Times of occupancy. The minimum rate of outdoor air required by Section 121(b)2 shall be supplied to each
space at all times when the space is usually occupied.
EXCEPTION 1 to Section 121(c)1: Demand control ventilation. In intermittently occupied spaces that do not
have processes or operations that generate dusts, fumes, mists, vapors or gasses and are not provided with local
exhaust ventilation (such as indoor operation of internal combustion engines or areas designated for unvented
food service preparation), the rate of outdoor air may be reduced if the ventilation system serving the space is
controlled by a demand control ventilation device complying with Section 121(c)4.
EXCEPTION 2 to Section 121(c)1: Temporary reduction. The rate of outdoor air provided to a space may be
reduced below the level required by Section 121(b)2 for up to 5 minutes each hour if the average rate for each
hour is equal to or greater than the required ventilation rate.
NOTE: VAV must comply with Section 121(c)1 at minimum supply airflow.
I am trying to find a similar edict for the State of Texas.
Any takers?
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
2154 Torrance Blvd, Ste. 100, Torrance, CA 90501
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/9d8f7a78/attachment.htm>
More information about the Equest-users
mailing list