[Equest-users] Texas OPERATIONAL Ventilation Requirements - eQuest Related
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Wed Jun 6 11:38:08 PDT 2012
ashrae 62.1-2004 section 5.4 ventilation controls. mechanical
ventilation systems shall include controls, manual or automatic, that
enable the fan system to operate whenever the spaces served are
occupied. the system shall be designed to maintain the minimum outdoor
airflow as required by section 6 under any load condition. note: vav
systems with fixed outdoor air damper positions must comply with this
requirement at minimum airflow.
ashrae 62.1-2007 user's manual, page 5-11. user's manual example also
explains why the 'auto' setting for fan on a basic thermostat does not
meet the requirement to provide outdoor air when the spaces is occupied
- the fan will cycle off when setpoint is reached and no outdoor air
will be supplied until the next call for cooling & the fan comes back on.
On 6/6/12 10:25 AM, John Aulbach wrote:
> Gang:
>
> I am trying to find where in the Texas Health and Safety Code where is
> says you must OPERATE ventilation in a certain manner, not just design
> a system to provide such ventilation. Tells me if i can reduce or
> eliminate exhaust air during certain times of the day (eQuest EEM).
>
> California Title-24, Subchapter 3, Section 121.c.1 specifically states:
>
> 1. Times of occupancy. The minimum rate of outdoor air required by
> Section 121(b)2 shall be supplied to each
> space at all times when the space is usually occupied.
> EXCEPTION 1 to Section 121(c)1: Demand control ventilation. In
> intermittently occupied spaces that do not
> have processes or operations that generate dusts, fumes, mists, vapors
> or gasses and are not provided with local
> exhaust ventilation (such as indoor operation of internal combustion
> engines or areas designated for unvented
> food service preparation), the rate of outdoor air may be reduced if
> the ventilation system serving the space is
> controlled by a demand control ventilation device complying with
> Section 121(c)4.
> EXCEPTION 2 to Section 121(c)1: Temporary reduction. The rate of
> outdoor air provided to a space may be
> reduced below the level required by Section 121(b)2 for up to 5
> minutes each hour if the average rate for each
> hour is equal to or greater than the required ventilation rate.
> NOTE: VAV must comply with Section 121(c)1 at minimum supply airflow.
>
> I am trying to find a similar edict for the State of Texas.
>
> Any takers?
>
> John R. Aulbach, PE, CEM
> Senior Energy Engineer
> ------------------------------------------------------------------------
> *Partner****Energy*
> 2154 Torrance Blvd, Ste. 100, Torrance, CA 90501
> W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
> www.ptrenergy.com <http://www.ptrenergy.com/>| jaulbach at ptrenergy.com
> <mailto:%7C%20jaulbach at ptrenergy.com>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/076d6347/attachment-0002.htm>
More information about the Equest-users
mailing list