[Equest-users] Texas OPERATIONAL Ventilation Requirements - eQuest Related
Chris Jones
cj at enersave.ca
Wed Jun 6 12:45:24 PDT 2012
A quick search reveals that the State of Texas adopted the IECC 2009
code effective April 2011. This document may provide some directions
as to OA control.
http://www.seco.cpa.state.tx.us/tbec/comres.php
At 01:25 PM 06/06/2012, John Aulbach wrote:
>Gang:
>
>I am trying to find where in the Texas Health and Safety Code where
>is says you must OPERATE ventilation in a certain manner, not just
>design a system to provide such ventilation. Tells me if i can
>reduce or eliminate exhaust air during certain times of the day (eQuest EEM).
>
>California Title-24, Subchapter 3, Section 121.c.1 specifically states:
>
>1. Times of occupancy. The minimum rate of outdoor air required by
>Section 121(b)2 shall be supplied to each
>space at all times when the space is usually occupied.
>EXCEPTION 1 to Section 121(c)1: Demand control ventilation. In
>intermittently occupied spaces that do not
>have processes or operations that generate dusts, fumes, mists,
>vapors or gasses and are not provided with local
>exhaust ventilation (such as indoor operation of internal combustion
>engines or areas designated for unvented
>food service preparation), the rate of outdoor air may be reduced if
>the ventilation system serving the space is
>controlled by a demand control ventilation device complying with
>Section 121(c)4.
>EXCEPTION 2 to Section 121(c)1: Temporary reduction. The rate of
>outdoor air provided to a space may be
>reduced below the level required by Section 121(b)2 for up to 5
>minutes each hour if the average rate for each
>hour is equal to or greater than the required ventilation rate.
>NOTE: VAV must comply with Section 121(c)1 at minimum supply airflow.
>
>I am trying to find a similar edict for the State of Texas.
>
>Any takers?
>
>John R. Aulbach, PE, CEM
>Senior Energy Engineer
>
>Partner Energy
>2154 Torrance Blvd, Ste. 100, Torrance, CA 90501
>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
><http://www.ptrenergy.com/>www.ptrenergy.com
><mailto:|%20jaulbach at ptrenergy.com>| jaulbach at ptrenergy.com
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/a34632ed/attachment-0002.htm>
More information about the Equest-users
mailing list