I use this option whenever applicable in my proposed and baseline systems.
I can't understand why it would cause an issue with the reviewer unless
you were trying to claim that your proposed system only used zone fans
while your baseline system 6 turned the AHU on.
As you say, the baseline system does not have zone fans and thus has no
option but to run the AHU at night. Your proposed system should be modeled
and controlled as described in the project documents. If the description
of operations states that the AHU will not activate on a call for night
heating, then the zone fans only option would be applicable.
Robby Oylear, PE, LEED AP
*Mechanical Engineer*
*Senior Energy Analyst*
* *
*D* 206-788-4571
*www.rushingco.com* <http://www.rushingco.com/>
On Wed, Jun 27, 2012 at 8:18 AM, Hall, Brendan <BHall at karpinskieng.com>wrote:
> Hey all,****
>
> ** **
>
> Has anyone ever had a model accepted that uses the NIGHT-CYCLE-CTRL = ZONE
> FANS ONLY option? I have an underfloor system that uses fan powered boxes
> at the perimeter zones for heat. I had tried the strategy on another
> project and it was rejected. The reason given was that because my baseline
> was system 6 and they said that it was a ECM inherent in having fan powered
> boxes. My current project is a system 5 so it would seem that the previous
> comment given would not apply. I want to try and use that strategy again
> but I wanted to know if anyone else had any experience trying to get that
> option accepted by a reviewer.****
>
> ** **
>
> ** **
>
> Brendan****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Cristian
> Salvador Jara Toro
> *Sent:* Wednesday, June 27, 2012 9:54 AM
> *To:* Javed Iqbal
> *Cc:* <equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] hvac systems acronyms on equest****
>
> ** **
>
> Hi, well, I should started in DOE2.2 manual... Thanks to both.
> *
> In my search I found this too:
>
> http://abraxasenergy.com/resources/toolbox/hvac-acronyms/
>
> best Regards!
>
> Cristian Jara Toro*
> Ingeniero Acústico
>
> Cel: 6 207 8566
>
>
>
> ****
>
> On Wed, Jun 27, 2012 at 9:11 AM, Javed Iqbal <eee.javed at gmail.com> wrote:*
> ***
>
> Hi,****
>
> ** **
>
> For VRF modeling you can follow this document.****
>
> ** **
>
> Thanks!****
>
> On Wed, Jun 27, 2012 at 6:32 PM, Cristian Salvador Jara Toro <
> cristian.jara.toro at gmail.com> wrote:****
>
> Dear All:
>
> I´m looking for a list where I could find every single hvac system
> described, like VRF, PVVT, etc. Hardly to familiarize with them, where
> systems and equipment are described in other language, so, my point is,
> let´s say, to make a parallel with them.
>
> any suggestions will be considered.
>
> best.
> *
>
> Cristian Jara Toro*
> Ingeniero Acústico
>
> Cel: 6 207 8566
>
>
> ****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
>
>
> ****
>
> ** **
>
> -- ****
>
> ** **
>
> ** **
>
> Javed Iqbal, LEED AP, CEA****
>
> Energy Analyst ****
>
> ** **
>
> ** **
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120627/c74e46ab/attachment-0002.htm>
More information about the Equest-users
mailing list