[Equest-users] [equest] Unmet load hours
Nick Caton
ncaton at smithboucher.com
Mon Mar 19 07:48:13 PDT 2012
My preference:
One can also, after a simulation, navigate to the air-side systems tab, highlight the top item ("project...") in the component tree on the left, then click the "summary" tab. If you have a lot of systems you can if you wish filter to a single system by highlighting just that system on the left. What you get is a summary report that pulls together a lot of figures you might otherwise have to dig around for. This is in my experience the easiest/quickest way to check zone and project unmet hour totals (summed at the bottom for the whole project). If you aren't familiar with the whole 'coincidental' vs. 'non-coincidental' unmet hours distinction, note the system-level sums can be misleading as they'll count the same hour multiple times for multiple zones.
I usually start here, and if I find one or more zones with too many hours I'll first try to identify any common spatial/system/envelope relationships that could be the root cause. Note the actual quantity and distribution of unmet hours are sometimes a very strong clue. If a likely cause is not apparent / readily testable from here, I'll investigate further with the detailed SS zone/system reports.
Following is a screenshot using v3.64 illustrating what I'm describing - project name scribbled out for sensitivity reasons:
[cid:image002.png at 01CD05B3.B58FD6C0]
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Saturday, May 08, 2010 6:33 PM
To: kce2 at kamalcogentenergy.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] [equest] Unmet load hours
also look in the SS-F reports. I use those first and then look at SS-R and then maybe SS-O.
pasha
On Fri, May 7, 2010 at 11:52 PM, Ashu <kce2 at kamalcogentenergy.com<mailto:kce2 at kamalcogentenergy.com>> wrote:
Sanjay,
You can find in ss-r report
Thanks,
Ashu
Sent from my Nokia phone
-----Original Message-----
From: Sanjay Cholekar
Sent: 08/05/2010 11:09:11 am
Subject: [Equest-users] [equest] Unmet load hours
In which report i could find Unmet load hours for zones and system?
Regards,
Sanjay Cholekar
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120319/6bac7cf1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120319/6bac7cf1/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 120584 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120319/6bac7cf1/attachment-0001.png>
More information about the Equest-users
mailing list