[Equest-users] 答复: what's the default equipment control?
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Thu Mar 22 06:28:32 PDT 2012
Joey –
I have had the same (counter-intuitive) experience. (ie load a, then load b+c, then load b+c+d …)
I didn’t end up solving it for my building. All my chillers were identical in capacity and part-load curve. I also had one chiller in the plant that never got turned on (ie my load never exceeded the capacity of my plant). Since those were the case, I assumed that the energy cost was the same as if there were a more intuitive control (load a, then load a+b, then load a+b+c). There appears to be an anamoly in your sample where “b” runs by itself for a while (why?) but as long as capacity, part load, etc are identical between chiller the outputs should be similar to the intuitive loading, I believe.
I did have to do a little explaining as to why the PS-C reports came out as they did.
Aaron
Aaron Dahlstrom , PE, LEED® AP
In Posse – A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jiao, Joey
Sent: Thursday, March 22, 2012 2:48 AM
To: John Aulbach; Equest-users at lists.onebuilding.org
Subject: [Equest-users] 答复: what's the default equipment control?
Hi John & everyone:
Thank you for your helps , I just check that, but it seems different than we thought.
The PS-H report show the chiller water loop run hours. I add it in the form, so you can get it clear.
Equipment control
Chiller 1a
Chiller 1b
Chiller 1c
Chiller Water Loop
None
2126
624
607
2750
Chiller1~3 to seq 1~3
2750
607
0
2750
All Chillers seq 1
2750
2750
2750
2750
Now you can find that , the loop run hours for all control types is 2750.
If the default control type as we thought , the chiller 1a should be 2750 equal to the run hours of Chiller Water Loop, because in any situation , the chiller 1a should first and always be used.
Maybe I think too much. But it is a software , I think there must be a sample and clear way for the default control.
Thank you for your help again.
Joey
发件人: John Aulbach [mailto:jra_sac at yahoo.com]<mailto:[mailto:jra_sac at yahoo.com]>
发送时间: 2012年3月22日 13:20
收件人: Jiao, Joey; Equest-users at lists.onebuilding.org<mailto:Equest-users at lists.onebuilding.org>
主题: Re: [Equest-users] what's the default equipment control?
Joey:
I am guessing, but I BELIEVE Chiller-1 gets to a certain load (think it's defined in the chiller setup), then Chiller-1 and Chiller-2 share the load until Chiller-3 is needed, when all three share the load.
See if that makes sense.
John Aulbach
Partner Energy
________________________________
From: "Jiao, Joey" <Joey.Jiao at WSPGroup.com.cn<mailto:Joey.Jiao at WSPGroup.com.cn>>
To: Equest-users at lists.onebuilding.org<mailto:Equest-users at lists.onebuilding.org>
Sent: Wednesday, March 21, 2012 7:49 PM
Subject: [Equest-users] what's the default equipment control?
Hi, everyone:
What’s the default equipment control when a loop with more than 1 plant?
At first I think the default should be” chiller1a- sequence 1, chiller 2a-sequence2, …” or all the chillers with the same sequence 1.
But my experiment shows it different than my think .
I make a system with 3 chiller and make a calculation under different control way.
The result run hour shows below:
Equipment control
Chiller 1a
Chiller 1b
Chiller 1c
None
2126
624
607
Chiller1~3 to seq 1~3
2750
607
0
All Chillers seq 1
2750
2750
2750
So I’m puzzled with how should the software control more than 1 plant when there is no equipment control set?
[cid:image001.png at 01CD080E.2649FD80]
Any suggestion should be appreciated.
Thank you very much.
Joey
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120322/942c71c5/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6739 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120322/942c71c5/attachment-0002.png>
More information about the Equest-users
mailing list