[Equest-users] Multi-use building LEED Baseline
Nick Caton
ncaton at smithboucher.com
Wed May 2 13:06:59 PDT 2012
Sounds like a fun project =)!
I would assign at least two baseline system types, split between residential (types 1,2) and non-residential areas (types 3+)
Each area's respective proposed system determines the heating source.
If all non-residential area proposed systems are 'fossil fuel' heating (depends on that boiler type), they will all use the same baseline system type, determined by their collective non-residential square footage and # of floors.
If that's an 'electric/other' boiler however, a third system type is in play, again selected based on the respective areas & floor quantities.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell
Sent: Wednesday, May 02, 2012 12:34 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Multi-use building LEED Baseline
We are currently modeling a multi-use building. This includes apartments, resident amenities, a Boys and Girls Club, and retail. Each of these areas have a different HVAC system (e.g. residential are heat pumps, retail/amenities are split-systems plus furnace, and Boys and Girls Club is central boiler system). Each of these four spaces are over 25,000 SF. In this case, how should the systems be layed out for the LEED baseline model?
Thanks,
Mike Campbell, EIT, LEED AP O+M
Sustainability Specialist
(610) 569-1047 office
(610) 569-1040 fax
mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>
www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
[Description: cid:image002.jpg at 01C81E05.97C02180]
[Description: WBE_cmyk_CP copy]
This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/fd448e7e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/fd448e7e/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 4667 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/fd448e7e/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 2004 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/fd448e7e/attachment-0008.jpg>
More information about the Equest-users
mailing list