[Equest-users] autosizing HVAC in baseline model
    Peter Baumstark 
    pbaumstark at sbcglobal.net
       
    Thu Oct 18 23:34:43 PDT 2012
    
    
  
Eva,
I think what you want is to, in DD mode, put the cooling capacity at 0 and the 
cool sizing ratio at 1.15 (I think that's what Appendix G specifies).  See the 
screen shot.
Does that answer your question?
________________________________
From: Evangelia Gklezakou <gklezakou.eva at gmail.com>
To: equest-users at lists.onebuilding.org
Sent: Thu, October 18, 2012 5:02:07 PM
Subject: [Equest-users] autosizing HVAC in baseline model
Dear Sirs,
I model the baseline case of a project and I need to calculate the capacity and 
the other parameters  of the HVAC (system 6). If I am not wrong I can do this by 
autosizing but I am in DD mode and so I do not have this option. Do I have to do 
parametric runs in order to calculate the required values? Any information 
regarding this procedure is going to be very useful.
Thank you for the help.
Regards,
Eva