The U-factor reported in the .sim file includes
the frame effects - if frames have been
modelled. If frames are modelled, each window may have a different U-factor
depending on the size of the window vs the amount
of framing. A smaller window will have a poorer U-factor.
The other issue is that the Simplified method
asks for the Glass Conductance - not the U-factor.
From the DOE22Vol2-Dictionary_47f.pdf manual:
GLASS-CONDUCTANCE
The conductance of the glazing, excluding the
outside air film coefficient. The conductance
given in glass manufacturers' data sheets usually
includes the outside air film resistance for a
wind speed of 7.5 mph (summer) or 15 mph
(winter). Table 10 can be used to obtain the
corresponding value of GLASS-CONDUCTANCE. For
example, if U(7.5 mph) = 0.64 Btu/ft2-hr-F, then
GLASS-CONDUCTANCE = 0.79 (by interpolation). For
Uvalues of different glazing types, see
manufacturers' data sheets or the ASHRAE 1989 Handbook of Fundamentals,
p. 27.16-17.
Emacs!
At 05:01 PM 03/09/2012, Andres Franco wrote:
>Content-Type: multipart/related;
> boundary="----=_NextPart_000_0010_01CD89ED.58B2F4F0"
>Content-Language: es-co
>
>Hi there, I´m working in a medium size project
>of a warehouse, apparently all in eQuest is
>working fine but when I saw the results for the
>glass in all my windows the U-Factor values are
>wrong, I want to know if somebody has already
>had this problem or if exists any formula or
>something for make an input accurately for the
>glass factor values in a correct way, thanks in advance, best regards.
>
>
>
>
>
>__________ Información de ESET NOD32 Antivirus,
>versión de la base de firmas de virus 7442 (20120903) __________
>
>ESET NOD32 Antivirus ha comprobado este mensaje.
>
><http://www.eset.com>http://www.eset.com
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120904/7a4b1a39/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 67b02d.jpg
Type: application/octet-stream
Size: 123373 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120904/7a4b1a39/attachment-0002.obj>
More information about the Equest-users
mailing list