Thanks Brian. I assume heat transfer between
plenum and space has the same issue in LS-B, LS-C?
At 11:28 AM 28/09/2012, Brian Fountain wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_00D9_01CD9D6C.572E3FD0"
>Content-Language: en-us
>
>I had a question yesterday regarding heat
>transfer through interior walls. I think this
>comes up on the list fairly frequently why is
>my LS-C (or LS-B) report showing no heat
>transfer across internal surfaces when I know my
>garage or attic is colder than the adjacent
>spaces. Is this heat loss really being
>reflected in the model and if so, why isnt it in the LOADS reports?
>
>Here was my answer (corrections & clarifications are welcome):
>
>What you are doing to model the effect of
>insulating the floor between the garage and the
>ground level is correct. eQUEST will calculate
>the heat loss across that interior surface floor
>and show the impact of the insulation. The main
>issue is finding it. I imagine you are looking
>at the LS-C or LS-B report which show no
>internal conduction. The issue here is how the
>calculations are sequenced in DOE-2. In the
>LOADS, we are calculating the envelope heat loss
>then in SYSTEMS we are calculating the HVAC
>response. But, until the HVAC response is
>calculated, we dont know what the space
>temperature is so we cant calculate the
>envelope heat loss as we dont know the delta-T
>between inside and outside. So, for LOADS, we
>give the space temperature an initial guess
>keyword Temperature in the SPACE. By default,
>all spaces have their temperature set to 70F
>this is why you see no internal heat loss in the
>LS- LOADS reports as the temperature is the same
>for all zones. You could set the annual average
>temperature down in the garage so that the heat
>loss shows here but it is not that
>important. As long as in the zones, the keyword
>SIZING-OPTION is set to ADJUST-LOADS then in
>SYSTEMS, the actual space temperature will be
>used to recalculate the heat loss.
>
>So, the heat loss is there you can reassure
>yourself of this by creating an interior wall of
>nearly infinite resistance, apply it as a
>parametric run, and see the space heating in the
>adjacent zones go down. You can also create
>hourly reports that look at the parameters of
>the zones. One of the hourly variables (23) at
>the zonal level is Contrib to the zone load due
>to conduction from adj zones (Btu/hr) -- this
>is where you will see the actual hourly heat
>loss using the actual hourly space temperature for the zones.
>
>I hope this helps clear up what you are
>seeing. Please feel free to ask more if I am not being clear.
>
>Kind regards,
>
>Brian
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
More information about the Equest-users
mailing list