Interior walls never have heat transfer, unless there is temperature change
more than 10 Deg F. Normally Garage are model as outside space, unless they
are heated or cooled.
Rashmi
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Jones
Sent: Friday, September 28, 2012 1:57 PM
To: Brian Fountain; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] FW: eQuest question on modelling interior
surface between floors
Thanks Brian. I assume heat transfer between plenum and space has the same
issue in LS-B, LS-C?
At 11:28 AM 28/09/2012, Brian Fountain wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_00D9_01CD9D6C.572E3FD0"
>Content-Language: en-us
>
>I had a question yesterday regarding heat transfer through interior
>walls. I think this comes up on the list fairly frequently - why is my
>LS-C (or LS-B) report showing no heat transfer across internal surfaces
>when I know my garage or attic is colder than the adjacent spaces. Is
>this heat loss really being reflected in the model - and if so, why
>isn't it in the LOADS reports?
>
>Here was my answer - (corrections & clarifications are welcome):
>
>What you are doing to model the effect of insulating the floor between
>the garage and the ground level is correct. eQUEST will calculate the
>heat loss across that interior surface floor and show the impact of the
>insulation. The main issue is finding it. I imagine you are looking
>at the LS-C or LS-B report which show no internal conduction. The
>issue here is how the calculations are sequenced in DOE-2. In the
>LOADS, we are calculating the envelope heat loss then in SYSTEMS we are
>calculating the HVAC response. But, until the HVAC response is
>calculated, we don't know what the space temperature is so we can't
>calculate the envelope heat loss as we don't know the delta-T between
>inside and outside. So, for LOADS, we give the space temperature an
>initial guess - keyword Temperature in the SPACE. By default, all
>spaces have their temperature set to 70F - this is why you see no
>internal heat loss in the
>LS- LOADS reports as the temperature is the same for all zones. You
>could set the annual average temperature down in the garage so that the
>heat loss shows here but it is not that important. As long as in the
>zones, the keyword SIZING-OPTION is set to ADJUST-LOADS then in
>SYSTEMS, the actual space temperature will be used to recalculate the
>heat loss.
>
>So, the heat loss is there - you can reassure yourself of this by
>creating an interior wall of nearly infinite resistance, apply it as a
>parametric run, and see the space heating in the adjacent zones go
>down. You can also create hourly reports that look at the parameters
>of the zones. One of the hourly variables (23) at the zonal level is
>"Contrib to the zone load due to conduction from adj zones (Btu/hr)"
>-- this is where you will see the actual hourly heat loss using the
>actual hourly space temperature for the zones.
>
>I hope this helps clear up what you are seeing. Please feel free to
>ask more if I am not being clear.
>
>Kind regards,
>
>Brian
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list