[Equest-users] LEED Fenestration Modeling Question
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Apr 15 11:45:11 PDT 2013
Paul,
I recently received the following comment in a LEED review for a LEED-NC v2009 project:
[cid:image001.png at 01CE39E7.4EDD07E0]
This implies that Window v6.3 calculations are acceptable in lieu of NFRC ratings. The comment does not exclude the modeler from performing the calculation.
Of course, I have no idea if this is boilerplate language or if LEED reviewers have discretion here. It is also possible that requirements will become stricter for newer projects.
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Monday, April 15, 2013 2:34 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Fenestration Modeling Question
Folks:
I am a bit confused when modeling unrated vertical fenestration for the proposed model. 90.1 states that we need to use the values determined in accordance with NFRC 100 or we can use the data in Table A8.2 for vertical fenestration per Exception b, Section 5.8.2.4.
If so, the values in Table A8.2 exceed the maximum allowed fenestration u-values listed in Table 5.5-5 (my zone), so will this not disqualify the proposed building model?
I have often found it impossible to get the architect to supply the NFRC assembly ratings of the glazing and field erected curtain-wall systems.
I have used the LBNL Window 6.3 program to calculate the vertical fenestration ratings, but 90.1 Section 5.8.8.2 states that the fenestration product shall have a permanently installed nameplate or the manufacturer shall provide a signed and dated certification for the installed fenestration.
I don't see any wiggle-room where 90.1 allows the modeler to calculate the NFRC rating of vertical fenestration.
Saying that, I have submitted projects where I calculated the fenestration assembly u-values without any kick-back from the GBCI.
I am concerned that the reviewers will push this issue since it is now clearly defined on the new Section 1.4 Table and if I submit my own ratings I will end up remodeling the project and/or the proposed building envelope will be rejected since it doesn't meet the mandatory requirements of Section 5.4.
Any thoughts?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com<http://www.pdigliollc.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130415/ca1d6b21/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 52818 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130415/ca1d6b21/attachment-0002.png>
More information about the Equest-users
mailing list