[Equest-users] LEED Fenestration Modeling Question
David Reddy
david.j.reddy1 at gmail.com
Mon Apr 15 13:24:23 PDT 2013
The NFRC CMAST database includes ratings for a growing number storefront
and curtainwall products, where ratings are generated using the NFRC
Component Modeling Approach (CMA). These are project-specific ratings
based on specific combinations of frame, glazing unit, and spacer, but
if they match your proposed design, I would guess that LEED would accept
these ratings as an acceptable substitute for your own WINDOW/THERM
analysis.
http://cmast.nfrc.org/Product/ProductFind.aspx
David
On 4/15/2013 12:34 PM, Paul Diglio wrote:
> Thanks Bill, the comment you received is encouraging.
> Paul Diglio, CEM, CBCP
>
> 87 Fairmont Avenue
> New Haven, CT 06513
> 203-415-0082
>
>
> www.pdigliollc.com <http://www.pdigliollc.com>
>
>
> ------------------------------------------------------------------------
> *From:* "Bishop, Bill" <bbishop at pathfinder-ea.com>
> *To:* Paul Diglio <paul.diglio at sbcglobal.net>;
> "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
> *Sent:* Mon, April 15, 2013 2:45:18 PM
> *Subject:* RE: [Equest-users] LEED Fenestration Modeling Question
>
> Paul,
>
> I recently received the following comment in a LEED review for a
> LEED-NC v2009 project:
>
> This implies that Window v6.3 calculations are acceptable in lieu of
> NFRC ratings. The comment does not exclude the modeler from performing
> the calculation.
>
> Of course, I have no idea if this is boilerplate language or if LEED
> reviewers have discretion here. It is also possible that requirements
> will become stricter for newer projects.
>
> Regards,
>
> Bill
>
> *William Bishop, PE, BEMP, LEED AP **|**Pathfinder Engineers &
> Architects LLP*
>
> Senior Energy Engineer
>
> 134 South Fitzhugh StreetRochester, NY 14608
>
> T: (585) 325-6004 Ext. 114F: (585) 325-6005
>
> bbishop at pathfinder-ea.com
> <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com
> <http://www.pathfinder-ea.com/>
>
> PSustainability -- the forest AND the trees.P
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Paul Diglio
> *Sent:* Monday, April 15, 2013 2:34 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] LEED Fenestration Modeling Question
>
> Folks:
>
> I am a bit confused when modeling unrated vertical fenestration for
> the proposed model. 90.1 states that we need to use the values
> determined in accordance with NFRC 100 or we can use the data in Table
> A8.2 for vertical fenestration per Exception b, Section 5.8.2.4.
>
> If so, the values in Table A8.2 exceed the maximum allowed
> fenestration u-values listed in Table 5.5-5 (my zone), so will this
> not disqualify the proposed building model?
>
> I have often found it impossible to get the architect to supply the
> NFRC assembly ratings of the glazing and field erected curtain-wall
> systems.
>
> I have used the LBNL Window 6.3 program to calculate the vertical
> fenestration ratings, but 90.1 Section 5.8.8.2 states that the
> fenestration product shall have a permanently installed nameplate or
> the manufacturer shall provide a signed and dated certification for
> the installed fenestration.
>
> I don't see any wiggle-room where 90.1 allows the modeler to calculate
> the NFRC rating of vertical fenestration.
>
> Saying that, I have submitted projects where I calculated the
> fenestration assembly u-values without any kick-back from the GBCI.
>
> I am concerned that the reviewers will push this issue since it is now
> clearly defined on the new Section 1.4 Table and if I submit my own
> ratings I will end up remodeling the project and/or the proposed
> building envelope will be rejected since it doesn't meet the mandatory
> requirements of Section 5.4.
>
> Any thoughts?
>
> Thank you,
>
> Paul Diglio, CEM, CBCP
>
> 87 Fairmont Avenue
> New Haven, CT 06513
> 203-415-0082
>
> www.pdigliollc.com <http://www.pdigliollc.com>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130415/85a87613/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 52818 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130415/85a87613/attachment-0002.png>
More information about the Equest-users
mailing list