[Equest-users] How to set the COP of a chiller as constant in eQuest?
Joe Huang
yjhuang at whiteboxtechnologies.com
Wed Apr 17 16:55:53 PDT 2013
Erik,
You're right. It should be a straight diagonal line from 0,0 to 1,1.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/17/2013 3:43 PM, Erik Kolderup wrote:
> Nick,
>
> One point of correction regarding curves to provide constant COP... I'm pretty sure you
> do not want the EIR-FPLR curve to be constant 1.0. The value of that curve is actually
> (normalized EIR)*(part load ratio). So if you want constant EIR, then the curve should
> just equal PLR. That's a straight line between (0,0) and (1,1). So the "a" coefficient
> should be zero and the "b" coefficient should be 1.0. All other coefficients for that
> curve should be zero.
>
> -Erik
>
> *Erik Kolderup, PE, LEED AP*
> erik at kolderupconsulting.com <mailto:erik at kolderupconsulting.com>| 415.531.5198
> <tel:415.531.5198> | www.kolderupconsulting.com <http://www.kolderupconsulting.com>
>
>
> ---------- Forwarded message ----------
> From: Nick Caton <ncaton at smithboucher.com <mailto:ncaton at smithboucher.com>>
> To: Joe Huang <yjhuang at whiteboxtechnologies.com
> <mailto:yjhuang at whiteboxtechnologies.com>>, Esmireta <e2fye2 at 163.com
> <mailto:e2fye2 at 163.com>>
> Cc: "equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>"
> <equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>>
> Date: Wed, 17 Apr 2013 19:40:31 +0000
> Subject: Re: [Equest-users] How to set the COP of a chiller as constant in eQuest?
>
> After identifying the curves in play per Joe’s suggestion, you could achieve a
> constant COP, independent of part load or other variables, by making a set of custom
> curves (of appropriate/acceptable type) using coefficient inputs.
>
> Example from the library:
>
> CentH2O-EIR-fPLR&dT looks like this from the library before modification. This
> curve works alongside others to determine how to modify the input EIR for a chiller:
>
> What we want is for this and all the other curves to return a value of 1.0, whatever
> the hourly variables throw at it. Simply enter all coefficients preceding a
> variable (b,c,d,e,f) to 0. Set the coefficient for the curve’s constant (a) at 1.0:
>
> Doing the same for all associated curves (again, read up in the help/documentation
> for your particular equipment to be sure), at all hours the chiller in question will
> operate at the specified EIR without variance.
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB**
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036 <tel:913.344.0036>
>
> fax 913.345.0617 <tel:913.345.0617>
>
> www.smithboucher.com <http://www.smithboucher.com>__
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130417/e5a6d609/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 31137 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130417/e5a6d609/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29199 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130417/e5a6d609/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130417/e5a6d609/attachment-0002.jpeg>
More information about the Equest-users
mailing list