[Equest-users] Questions Regarding SS-N and SS-O Reprts andUnoccupied Heating and Hummidty Requirements Results and How Do I Cycle the SUPPLY-KW/FLOW Value?
Kathryn Kerns
kathryn.kerns at bceengineers.com
Fri Apr 19 09:04:13 PDT 2013
Everyone, after stumbling around a little, I discovered that
eQuest/DOE-2 does take into account the maximum relative humidity limit
during unoccupied hours and operates the zone HVAC fan energy, cooling
and heating with the OSA closed. I figured this out by running the fan
system 24/7 (it was running 24/7 anyway according to SS-C) and noticing
that the total energy consumption did not change. Humidity and
temperature data then appeared in SS-N and SS-O reports. I also found
some help files that state that 0 in the MinOA schedule means closed OSA
so I know there is no OSA going into the pool area at night. So the
model I had was working fine, I just couldn't prove it. Running the HVAC
system 24/7 proves it.
So, now I am at the point of introducing my dehumidifier system to the
pool zone. I am planning on using the pool PSZ HVAC cooling coil to
represent the dehumidifier cooling coil since the specified PSZ HVAC
does not use a cooling coil. What I would like to do, is decrease the
PSZ SUPPLY-KW/FLOW value during unoccupied hours to represent the lower
dehumidifier fan rate. Does anybody know how to do this? In other words,
I want the pool zone PSZ HVAC supply fan to run at 0.0007 kw/cfm during
the day and run at 0.0003 kw/cfm during unoccupied hours. If I can't
change SUPPLY-KW/FLOW, is there a way to develop a schedule that
DECREASES the electric load by some amount during unoccupied hours? I
have found ways to add a load, but not subtract.
Thanks in advance.
James, I am not sure what you are trying to do? Condenser heat rejection
from what? A water to air heat pump?
Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 |
________________________________
From: James Hess [mailto:JHess at tmecorp.com]
Sent: Thursday, April 18, 2013 7:53 PM
To: Kathryn Kerns; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Questions Regarding SS-N and SS-O Reprts
andUnoccupied Heating and Hummidty Requirements
Pools are interesting to model. We are working on a project right now
with one. One challenge we have is how/where to get the heat recovery
data from the equipment vendors that sell the systems that can provide
condenser heat rejection for use in heating the pool. I'm sure we will
figure that out at some point.
For your project, I would recommend creating an hourly report for that
zone with zone temp and humidity. Then run eQuest, export hourly
report, and then analyze to see what's going on.
Can you please let us know what you find out? The community at large
might be interested in knowing.
Here are some "Thermal Zone" variables that might be useful for
diagnosing the operation.
Export hourly results:
Regards,
JAH
James A. Hess, PE, CEM, BEMP
Energy Engineer
TME, Inc.
Little Rock, AR
Mobile: (501) 351-4667
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn
Kerns
Sent: Thursday, April 18, 2013 6:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Questions Regarding SS-N and SS-O Reprts and
Unoccupied Heating and Hummidty Requirements
Everyone, I have an indoor pool in Alaska. I have figured out how to
model the pool's 24/7 latent load and required the pool area HVAC system
to maintain 88 F even for Night Cycle. I also gave the pool HVAC the
task of maintaining 60% max RH. The SS-C report shows the pool HVAC fan
running 8747 hours out of the year, 2357 of those hours running during
unoccupied hours. This is what I expected. I looked at the SS-O and SS-N
reports for my pool area and pool HVAC and noticed that 6390 hours of
temperature and relative humidity data are showing up, not 8740 hours.
In other words all the 2357 unoccupied hours are not showing up. How do
I verify if my pool HVAC system succeeded in managing to keep 88 F and
below 60% RH during the unoccupied period? I assume it can manage the
temperature problem, but how well did it manage the humidity problem? Or
did it just bag the humidity problem, in which case, do I have to run
the fan system 24/7 to get it to pay attention to the 60% max RH?
If I have to run the fan system 24/7 will that 0 value in the MinOA WD
schedule keep the outside from coming on or do I need to change it to a
positive number? If so, which positive number? 999?
Peculiar questions, I know.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130419/e0c3b604/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13099 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130419/e0c3b604/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 58978 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130419/e0c3b604/attachment-0005.jpeg>
More information about the Equest-users
mailing list