[Equest-users] How to set the COP of a chiller as constant in eQuest?
Esmireta
e2fye2 at 163.com
Sun Apr 21 21:49:56 PDT 2013
Hi Joe,
Thanks for your reply!
Is the DOE-2.2 manual the DOE help in the eQuest?
Esmi
At 2013-04-18 03:17:00,"Joe Huang" <yjhuang at whiteboxtechnologies.com> wrote:
Do you not have a copy of a DOE-2.2 or DOE-2.1E manual? That would make it hard to understand how DOE-2 works.
DOE-2 has many performance curves, depending on the type of equipment. The EIR-FT curves are either bi-linear or bi-quadratic functions of the entering wetbulb and outdoor drybulb temperature. The EIR-FPLR curves can be linear, quadratic, or cubic functions of the Part Load Ratio (PLR).
By the way,what I said yesterday was in reference to packaged SYSTEMS. If your model contains a PLANT model with a Chiller, then
the keywords for the chiller performance curves change somewhat.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.comwww.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/16/2013 11:09 PM, Esmireta wrote:
Hi Joe,
In the simulation of a district cooling system, the guidance requires a virtual plant with a constant average efficiency.
In the DOE curves, how can I know the meaning of the equation and the coefficients in it? It seems there is no useful information in the DOE help.
Thanks!
Esmi
At 2013-04-17 10:35:35,"Joe Huang" <yjhuang at whiteboxtechnologies.com> wrote:
DOE-2 modifies the COOL-EIR using several curves COOL-EIR-FT as a function of outdoor conditions and COOL-EIR-FPLR as a function of the Part Load Ratio. I suppose you could set those to be constant. Another way would be to just take the Cooling Load from the SS-D report and divide that by your constant COP. But my question would be, why do you want to do that ?
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.comwww.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/16/2013 6:55 PM, Esmireta wrote:
Dear all,
I wonder how to set the COP of a chiller as constant? after I set the chiller type, the electric input ratio type is determined, which means the self-made constant curve cannot be input.
Thanks!
Esmi
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/73e2e027/attachment-0002.htm>
More information about the Equest-users
mailing list