[Equest-users] How to set the COP of a chiller as constant in eQuest?
Joe Huang
yjhuang at whiteboxtechnologies.com
Mon Apr 22 08:38:48 PDT 2013
I was referring to the DOE-2 Supplement, Version 2.1E, produced by LBNL in 1993
(LBL-34947). I have not looked at the help function of eQUEST, so I can't tell how
detailed is it.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/21/2013 9:49 PM, Esmireta wrote:
> Hi Joe,
> Thanks for your reply!
> Is the DOE-2.2 manual the DOE help in the eQuest?
> Esmi
>
>
>
>
>
> At 2013-04-18 03:17:00,"Joe Huang" <yjhuang at whiteboxtechnologies.com> wrote:
>
> Do you not have a copy of a DOE-2.2 or DOE-2.1E manual? That would make it hard to
> understand how DOE-2 works.
> DOE-2 has many performance curves, depending on the type of equipment. The EIR-FT
> curves are either bi-linear or bi-quadratic functions of the entering wetbulb and
> outdoor drybulb temperature. The EIR-FPLR curves can be linear, quadratic, or cubic
> functions of the Part Load Ratio (PLR).
>
> By the way,what I said yesterday was in reference to packaged SYSTEMS. If your model
> contains a PLANT model with a Chiller, then
> the keywords for the chiller performance curves change somewhat.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com
> www.whiteboxtechnologies.com
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
>
> On 4/16/2013 11:09 PM, Esmireta wrote:
>> Hi Joe,
>> In the simulation of a district cooling system, the guidance requires a virtual
>> plant with a constant average efficiency.
>> In the DOE curves, how can I know the meaning of the equation and the coefficients
>> in it? It seems there is no useful information in the DOE help.
>> Thanks!
>> Esmi
>>
>>
>>
>>
>>
>> At 2013-04-17 10:35:35,"Joe Huang" <yjhuang at whiteboxtechnologies.com> wrote:
>>
>> DOE-2 modifies the COOL-EIR using several curves COOL-EIR-FT as a function of
>> outdoor conditions and COOL-EIR-FPLR as a function of the Part Load Ratio. I
>> suppose you could set those to be constant. Another way would be to just take
>> the Cooling Load from the SS-D report and divide that by your constant COP. But
>> my question would be, why do you want to do that ?
>>
>> Joe
>>
>> Joe Huang
>> White Box Technologies, Inc.
>> 346 Rheem Blvd., Suite 108D
>> Moraga CA 94556
>> yjhuang at whiteboxtechnologies.com
>> www.whiteboxtechnologies.com
>> (o) (925)388-0265
>> (c) (510)928-2683
>> "building energy simulations at your fingertips"
>>
>>
>> On 4/16/2013 6:55 PM, Esmireta wrote:
>>> Dear all,
>>> I wonder how to set the COP of a chiller as constant? after I set the chiller
>>> type, the electric input ratio type is determined, which means the self-made
>>> constant curve cannot be input.
>>> Thanks!
>>> Esmi
>>>
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/763652db/attachment-0002.htm>
More information about the Equest-users
mailing list