[Equest-users] Baseline Model - Modeling Chilled Water from Utility
Robby Oylear
robbyoylear at gmail.com
Mon Aug 26 11:38:35 PDT 2013
I tried running your model and actually had a different error terminate the
run:
***ERROR***********************************************************************
Loop: Hot Water Loop has zero design flow.
Check input for consistency, or specify design loads.
It looks like your VAV systems are setup with no reheat coils, which may or
may not be accurate to what you're trying to model. Based on your inputs
though, the only time the system would ever go into heating is when ALL the
zones need heating which is rather unlikely for a VAV system serving 20
zones.
I was able to get your model to simulate properly by using reheat coils and
giving it a delta T on the reheat temperature. If you don't actually have
reheat, then maybe consider using a preheat coil, not a heating coil, to
model the heating being done at the central air handler.
See attached for the .inp with my edits so you can see it running.
Again - I wasn't able to replicate your chilled water primary equipment
error so I apologize if this doesn't solve your issue!
[image: Inline image 1]
On Mon, Aug 26, 2013 at 9:51 AM, Dwight Pederson <dpederson at aeieng.com>wrote:
> Hello,****
>
> ** **
>
> I’m working on a building that has a chilled water utility instead of a
> chilled water plant. I set up a chilled water meter to measure the
> economics of the system and did not specify any chillers in the system.
> When I run the simulation the detailed simulation output file gives an
> error saying “Chilled water loop has no attached primary cooling
> equipment,” any thoughts out there as to why I am getting this error. I
> attached my .inp file to reference.****
>
> ** **
>
> Thanks,****
>
> ** **
>
> Dwight****
>
> ** **
>
> *Dwight Pederson** *EIT
> Mechanical****
>
> ****
>
> *AEI* | AFFILIATED ENGINEERS, INC.
> 4747 N. 7th Street, Suite 240 | Phoenix, AZ 85014
>
> P: 602.200.1030
> dpederson at aeieng.com | *www.aeieng.com* ****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130826/c9bec32d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29045 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130826/c9bec32d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: U of AZ .inp
Type: application/octet-stream
Size: 896178 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130826/c9bec32d/attachment-0002.obj>
More information about the Equest-users
mailing list