[Equest-users] Space type total square footage

Bishop, Bill bbishop at pathfinder-ea.com
Tue Dec 3 11:17:50 PST 2013


Gerry,
Here is one way to find area by space type in DD Edit Mode:

1.)    Export a Space Loads Report, and open it in Excel
[cid:image002.jpg at 01CEF032.71E1AF50]


2.)    Select all the rows with Spaces, and the column labels (starting with row 8) and Sort by "Activity Description".



3.)    Select all the cells for Activity Description and Area, including the column labels

[cid:image003.jpg at 01CEF032.71E1AF50]



4.)    Use the SUBTOTAL function in the Outline section of the Data tab
[cid:image004.jpg at 01CEF032.71E1AF50]

                Viola!

Regards,
Bill


William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[webCertified_logo_colorRGB72DPI.jpg]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 325-6004 Ext. 114            F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

P   Sustainability - the forest AND the trees. P



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, December 03, 2013 2:07 PM
To: Grace Pedersen; 'Gerard Hazel'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Space type total square footage

I think in many cases the DD wizard input screens are the easiest place to go, even post-wizards (just be sure to save separately first before going back, or else don't hit the wizard "finish" button).

Post-wizards, you could navigate to the spreadsheet view for your spaces which lists the occupancy description and space area (I believe this is one of those where you have to scroll right to find it), then select all and copy/paste into excel to organize the rows by space description type, then do some manual sums/algebra to come up with the intended area subtotals.

I think wizards are almost certainly the easier approach between the two, for most cases.

~Nick

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Grace Pedersen
Sent: Tuesday, December 03, 2013 12:28 PM
To: 'Gerard Hazel'; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Space type total square footage

Hi Gerry,

Which design mode are you in? You can find it in the Zone Group Definitions Screen in the Design Development Wizard.

Grace

Grace Pedersen
UIC Energy Resources Center (MC 156)
1309 S. Halsted St, Suite 219
Chicago, IL 60607
Office: (312) 996-8324
Cell: (630) 276-8602
Fax: (312) 996-5620



From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gerard Hazel
Sent: Tuesday, December 03, 2013 12:16 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Space type total square footage

Hi All,
Does anyone know where I can find  the total square footage for each space type? i.e  Restrooms, Mechanical/Electrical, Office, etc?
Thanks,
Gerry Hazel


Gerard Hazel
M&E Engineers, Inc.
908-526-5700 x14

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 14205 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 28546 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 34512 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131203/a2a30037/attachment-0014.jpg>


More information about the Equest-users mailing list