[Equest-users] eQUEST fan power reporting
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Dec 23 09:13:04 PST 2013
I believe there are a couple things going on. First, PS-E reports the actual coincident peak fan power, while the HVAC Summary csv gives design values. Second, added static pressure from ERV is not included in the HVAC Summary csv, but is reflected in PS-E.
~Bill
From: Christian Stalberg [mailto:christian at naturalintelligence.us]
Sent: Monday, December 23, 2013 11:53 AM
To: Bishop, Bill; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] eQUEST fan power reporting
Bill,
Sorry! I meant to say that the MAX KW reported for Vent Fans in the PS-E Energy End-Use Summary for all Electric Meters report is different than the supply and return energy usage reported under Fan Summary in the HVAC Summary csv report. What is that/what would explain the difference?
Thanks!
_
Christian Stalberg
Natural Intelligence, LLC
http://naturalintelligence.us
Tel. 415.531.4610
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Monday, December 23, 2013 11:44 AM
To: Christian Stalberg; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] eQUEST fan power reporting
Christian,
Maybe we're looking at different reports, but the Fan Summary section of the HVAC Summary report only shows power (kW) in my reports, while BEPU shows energy (kWh).
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Christian Stalberg
Sent: Monday, December 23, 2013 10:58 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQUEST fan power reporting
Can anyone explain to me why the vent fans electric usage in the BEPU report and the supply and return energy usage under Fan Summary in the HVAC Summary csv report are different?
For a VAV system with PFP boxes I am assuming the zone fan data is not included in the HVAC Summary csv report. This data is reported in the SIM SV-B report.
Thanks in advance.
_
Christian Stalberg
Natural Intelligence, LLC
http://naturalintelligence.us
Tel. 415.531.4610
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131223/752829ef/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131223/752829ef/attachment-0002.jpg>
More information about the Equest-users
mailing list