[Equest-users] Existing Building - New Windows
Harmon, Amy
aharmon at sbmce.com
Wed Feb 6 12:49:47 PST 2013
I've been scouring the archives for answers, but did not find my exact scenario.
I have a 10 story dormitory that was built in the early 60's. We're looking to submit the building to LEED. We're removing the existing 2 pipe FCU system serving the perimeter rooms as well as an AHU that conditions the core spaces for the whole building, with a 4 pipe FCU system along the perimeter rooms (natural windows via operable windows) and an AHU for the core spaces in the building.
A couple questions, the architect is replacing all the windows in the building. Since the proposed case windows will be what we're designing to, what windows do I use for my baseline...existing as it stands today or the ASHRAE minimum found in Table 5.5?
The architect is also adding metal panels to portions of the building to dress it up, how do you go about adding the metal panels (UNINSULATED) to the existing wall used in the baseline?
Thanks for helping!
Amy Harmon
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Office: (330) 896-4664 x107
Direct: (330) 526-2707
Fax: (330) 896-9180
aharmon at sbmce.com<mailto:aharmon at sbmce.com>
www.sbmce.com<http://www.sbmce.com/>
Columbus Office (614) 448-1498
ü Please consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally privileged. If you are not an intended recipient or an authorized representative of an intended recipient, you are prohibited from using, copying or distributing the information in this e-mail or its attachments. If you have received this e-mail in error, please notify the sender immediately by return e-mail and delete all copies of this message and any attachments.
Thank you
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130206/51dda1a8/attachment.htm>
More information about the Equest-users
mailing list