Hi Neeraj,
To model this in eQuest you would go to the air-side system -> fans -> night cycle control  and set night ventilation to unavailable and fan cycle to the appropriate control scheme.
If you want to confirm this setup using the outputs from eQuest, I believe you will need to set up hourly reports for the systems and take a look there. To my knowledge, it doesn't show up explicitly in the .sim file. As a first approximation, you could check the SS-K report, and see if there is any difference between "temperature between outdoor & room air all hours" and "temperature difference between outdoor & room air fan off hours" which could suggest whether there is some sort of difference between "all hours" and "fan off hours" in the eyes of the model.
Alex
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of neeraj arora
Sent: Thursday, February 14, 2013 4:52 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How to verify that outside air is modeled with zero flow
Hi friends,
How to verify that outside air is modeled (in eQuest) with zero flow in both the Baseline and Proposed Case during unoccupied periods when fans are cycled on to meet unoccupied setback temperatures?
And how to model it in eQuest actually?
I got this comment from the reviewer in one of our projects.
Thanks in advance.