[Equest-users] How to verify that outside air is modeled with zero	flow
    Sami, Vikram 
    Vikram.Sami at perkinswill.com
       
    Thu Feb 14 10:36:34 PST 2013
    
    
  
I think the way to  do this is to set the night fans to cycle on any and set an  OA Schedule (like so):
[cid:image001.png at 01CE0AB8.31F6EF50]
MIN-AIR-SCH
Takes the U-name of a SCHEDULE that contains hourly values of the ratio of minimum outside air flow to supply air flow. Values in the MIN-AIR-SCH vary from 0.0 (no outside air flow; economizer inactive if specified) to 1.0 (100% outside air flow). A value of 0.001 actives the economizer. A value of -999 returns the hourly value to MIN-OUTSIDE-AIR or to the program's calculated minimum outside air value (found on report SV-A for the SYSTEM or for each zone for zonal systems). During a warmup period, this schedule is normally set to zero and can then be set to -999 during other hours to allow the specified or calculated ventilation minimum damper position to be used. Note that schedules are ignored in the design routines; therefore, the minimum ventilation air desired for design must be specified either at the zone or system level.
[cid:image002.png at 01CE0AB8.31F6EF50]
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Blue
Sent: Thursday, February 14, 2013 12:02 PM
To: neeraj arora; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] How to verify that outside air is modeled with zero flow
Hi Neeraj,
To model this in eQuest you would go to the air-side system -> fans -> night cycle control  and set night ventilation to unavailable and fan cycle to the appropriate control scheme.
If you want to confirm this setup using the outputs from eQuest, I believe you will need to set up hourly reports for the systems and take a look there. To my knowledge, it doesn't show up explicitly in the .sim file. As a first approximation, you could check the SS-K report, and see if there is any difference between "temperature between outdoor & room air all hours" and "temperature difference between outdoor & room air fan off hours" which could suggest whether there is some sort of difference between "all hours" and "fan off hours" in the eyes of the model.
Alex
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of neeraj arora
Sent: Thursday, February 14, 2013 4:52 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How to verify that outside air is modeled with zero flow
Hi friends,
How to verify that outside air is modeled (in eQuest) with zero flow in both the Baseline and Proposed Case during unoccupied periods when fans are cycled on to meet unoccupied setback temperatures?
And how to model it in eQuest actually?
I got this comment from the reviewer in one of our projects.
Thanks in advance.
Neeraj Arora
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130214/096e7de4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 55400 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130214/096e7de4/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 68631 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130214/096e7de4/attachment-0005.png>
    
    
More information about the Equest-users
mailing list