Thanks David and Nick. Your advice is much appreciated.
- MRH
On 2/27/2013 1:58 PM, Nick Caton wrote:
>
> No direct answers, but I would plan on a long discussion with the HVAC 
> designers to arrive at a mutual understanding of the "conditioned 
> volume" and loads incident on that volume to be addressed by the 
> systems.  Approaching this as thermally-connected 
> conditioned/unconditioned zones matching those design parameters makes 
> sense procedurally from an eQuest standpoint.
>
> Time permitting, running an early "test" model to ensure the results 
> agree/ballpark with the designer's calculations would be a good idea 
> as well to nail down the nuts & bolts of your modeling procedure 
> before crunch time (Keeping good notes & written communication will 
> also be helpful later for model documentation).
>
> cid:489575314 at 22072009-0ABB**
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com__
>
> *From:*equest-users-bounces at lists.onebuilding.org 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Matt Hein
> *Sent:* Wednesday, February 27, 2013 10:32 AM
> *To:* Email question to eQuest
> *Subject:* [Equest-users] Indoor arena suggestions/tips
>
> Hello all,
>
> I'm working on an 150,000 sf indoor practice facility with 90 ft 
> ceilings. Does anyone have any suggestions/tips/heads-up comments that 
> would be useful in starting this model?
> Specifically, I'm wondering if I'll run into issues related to 
> stratification and need to create 'sub-zones' so eQuest better 
> represents the proposed distribution system.
>
> Thank you for your time and combined insight,
>
> *Matthew Hein*, P.E.
> BTU Engineering, Inc.
> 2021 25^th Ave.
> Brookings, SD  57006
>
> Direct Phone: 605.695.8582
> Toll Free: 888.288.2126
> Fax: 888.288.2139
> matthew.hein at btu-engineering.com <mailto:hein at BTU-Engineering.com>
>
> www.BTU-Engineering.com <http://www.btu-engineering.com/>
>
> LinkedIn 
> <http://www.linkedin.com/company/2439091?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> 
> | Facebook 
> <https://www.facebook.com/BTU.Engineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> 
> | Google+ 
> <https://plus.google.com/112692580402915348575/posts?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> | 
> Twitter 
> <https://twitter.com/BTUEngineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> 
> | Subscribe to Email List <http://eepurl.com/uWeS9>
>
On 2/27/2013 10:50 AM, David Eldridge wrote:
>
> eQUEST will assume a uniform temperature throughout the zone, so if 
> the proposed HVAC system will allow stratification then you would need 
> to do something like you are describing.
>
> David
>
> __
>
> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
>
> *Grumman/Butkus Associates*
>
> __
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130227/533ff587/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130227/533ff587/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list