[Equest-users] Indoor arena suggestions/tips
Matt Hein
matthew.hein at btu-engineering.com
Thu Feb 28 08:23:50 PST 2013
Has anyone been able to capture savings from a natural ventilation
design for LEED 2009 NC? (I interpret that G3.1.1.b prevents this.)
Glancing over Appendix G I see something that doesn't seem very
encouraging of 'green' design: (not to say that it discourages)
* G3.1.1.b says, "All conditioned spaces in the proposed design shall
be simulated as being both heated and cooled even if no heating or
cooling system is to be installed ..."
It seems like there should be some way to encourage natural ventilation
design by accounting for the energy savings.
I suspect I'll approach this by setting a high Tstat value (100 F) and
using the exact same cooling configuration for proposed and baseline so
the savings are null. Well, maybe I can get some fan power savings.
- MRH
On 2/28/2013 8:33 AM, RobertWichert wrote:
> I would certainly bring it up. I would expect it to be more
> comfortable and with much lower fuel costs. Even first cost could be
> lower, if you really plan to heat all that air, unless the insulation
> is very heavy, even on the roof. I would think you could get away
> with minimal insulation on the roof if you used radiant.
>
> Just my first thought though, I'm sure there is much more to consider.
>
>
> Maybe you could keep us apprised of your progress...
>
>
>
> Robert Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
>
>
>
>
>
> ===============================================
> On 2/27/2013 2:47 PM, Matt Hein wrote:
>> The preliminary design calls for forced-air with low winter setpoint
>> of 60F and additional fans to de-stratify. Summer is Nat. ventilation
>> with no cooling.
>> I plan on discussing radiant heat in our next conversation.
>>
>> Thanks Robert,
>>
>> - MRH
>>
>> On 2/27/2013 4:02 PM, RobertWichert wrote:
>>> Is radiant heating being discussed, Matt?
>>>
>>>
>>> Robert Wichert P.Eng. LEED AP BD&C
>>> +1 916 966 9060
>>> FAX +1 916 966 9068
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> ===============================================
>>> On 2/27/2013 1:27 PM, Matt Hein wrote:
>>>> Thanks David and Nick. Your advice is much appreciated.
>>>>
>>>> - MRH
>>>>
>>>>
>>>>
>>>> On 2/27/2013 1:58 PM, Nick Caton wrote:
>>>>>
>>>>> No direct answers, but I would plan on a long discussion with the
>>>>> HVAC designers to arrive at a mutual understanding of the
>>>>> "conditioned volume" and loads incident on that volume to be
>>>>> addressed by the systems. Approaching this as thermally-connected
>>>>> conditioned/unconditioned zones matching those design parameters
>>>>> makes sense procedurally from an eQuest standpoint.
>>>>>
>>>>> Time permitting, running an early "test" model to ensure the
>>>>> results agree/ballpark with the designer's calculations would be a
>>>>> good idea as well to nail down the nuts & bolts of your modeling
>>>>> procedure before crunch time (Keeping good notes & written
>>>>> communication will also be helpful later for model documentation).
>>>>>
>>>>> cid:489575314 at 22072009-0ABB**
>>>>>
>>>>> **
>>>>>
>>>>> *NICK CATON, P.E.*
>>>>>
>>>>> SENIOR ENGINEER
>>>>>
>>>>> Smith & Boucher Engineers
>>>>>
>>>>> 25501 west valley parkway, suite 200
>>>>>
>>>>> olathe, ks 66061
>>>>>
>>>>> direct 913.344.0036
>>>>>
>>>>> fax 913.345.0617
>>>>>
>>>>> www.smithboucher.com__
>>>>>
>>>>> *From:*equest-users-bounces at lists.onebuilding.org
>>>>> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
>>>>> *Matt Hein
>>>>> *Sent:* Wednesday, February 27, 2013 10:32 AM
>>>>> *To:* Email question to eQuest
>>>>> *Subject:* [Equest-users] Indoor arena suggestions/tips
>>>>>
>>>>> Hello all,
>>>>>
>>>>> I'm working on an 150,000 sf indoor practice facility with 90 ft
>>>>> ceilings. Does anyone have any suggestions/tips/heads-up comments
>>>>> that would be useful in starting this model?
>>>>> Specifically, I'm wondering if I'll run into issues related to
>>>>> stratification and need to create 'sub-zones' so eQuest better
>>>>> represents the proposed distribution system.
>>>>>
>>>>> Thank you for your time and combined insight,
>>>>>
>>>>> *Matthew Hein*, P.E.
>>>>> BTU Engineering, Inc.
>>>>> 2021 25^th Ave.
>>>>> Brookings, SD 57006
>>>>>
>>>>> Direct Phone: 605.695.8582
>>>>> Toll Free: 888.288.2126
>>>>> Fax: 888.288.2139
>>>>> matthew.hein at btu-engineering.com <mailto:hein at BTU-Engineering.com>
>>>>>
>>>>> www.BTU-Engineering.com <http://www.btu-engineering.com/>
>>>>>
>>>>> LinkedIn
>>>>> <http://www.linkedin.com/company/2439091?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
>>>>> | Facebook
>>>>> <https://www.facebook.com/BTU.Engineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
>>>>> | Google+
>>>>> <https://plus.google.com/112692580402915348575/posts?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> |
>>>>> Twitter
>>>>> <https://twitter.com/BTUEngineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
>>>>> | Subscribe to Email List <http://eepurl.com/uWeS9>
>>>>>
>>>>
>>>> On 2/27/2013 10:50 AM, David Eldridge wrote:
>>>>>
>>>>> eQUEST will assume a uniform temperature throughout the zone, so
>>>>> if the proposed HVAC system will allow stratification then you
>>>>> would need to do something like you are describing.
>>>>>
>>>>> David
>>>>>
>>>>> __
>>>>>
>>>>> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
>>>>>
>>>>> *Grumman/Butkus Associates*
>>>>>
>>>>> __
>>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> Equest-users mailing list
>>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130228/4c5a9ed3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130228/4c5a9ed3/attachment-0002.jpeg>
More information about the Equest-users
mailing list