[Equest-users] Baseline system 5 vs wshp
    Bishop, Bill 
    bbishop at pathfinder-ea.com
       
    Fri Jan  4 06:11:21 PST 2013
    
    
  
Allen,
Without knowing anything else about the project, one thing that comes to mind is that maybe the Baseline should be System 6 because your predominant condition is electric-only heating. This could be the case unless you have boilers supplementing the heat pump loop, or if you have gas-fired DOAS. 60% is possible if, for example, you have heat recovery and the baseline doesn't require it, and you are in a heating-dominated climate. If you post your .pd2 and .inp files to the list, you never know who will take a look and provide some quick feedback.
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Allen Spencer
Sent: Friday, January 04, 2013 8:43 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline system 5 vs wshp
Hello Equest-Users,
We have submitted a project for LEED and have received feedback that states the energy savings ( in therms ) is unsubstantiated. Has anyone else compared a vav w/ reheat system to a wshp system? Our model shows a 60% savings in therms, does this seem excessive? I've checked the inputs and can't see why this might be happening.  Any help would be greatly appreciated. Thanks.
Allen Spencer
Rabideau Architects
550 Hinesburg Rd | Suite 101 | South Burlington, VT
802-863-0222 | allen at rabideau-architects.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130104/0fe6a2e5/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130104/0fe6a2e5/attachment-0002.jpg>
    
    
More information about the Equest-users
mailing list