[Equest-users] Beginner Question on Fan schedule
    Chris Jones 
    cj at enersave.ca
       
    Sun Jan 27 14:10:39 PST 2013
    
    
  
I don't think the behavior of INTERMITTENT changed from DOE2.1e to 
DOE2.2.  The DOE2.1e Supplement has the same wording as the DOE2.2 manual.
I would add some hourly reports - supply cfm, OA ratio, heating 
energy and cooling energy.   Run for both CONTINUOUS and 
INTERMITTENT.  There may be some differences in the amount of outdoor 
air that is being introduced.
At 11:20 AM 27/01/2013, RobertWichert wrote:
>Thanks for the link to the manuals and such, Chris.
>
>I am also investigating "intermittent" as it affects EnergyPro, 
>which claims to use "DOE-2.1E* v119".
>
>The issue involves using "INTERMITTENT" and how that affects heating 
>energy.  Heating energy drops dramatically when "INTERMITTENT" is 
>invoked.  It drops so far that it does not seem realistic, although 
>no errors or flags result that I can find.
>
>I have found some references to "INTERMITTENT" causing negative 
>CFM: 
><http://doe2.com/download/DOE-22/Bugfixes-047h.pdf>http://doe2.com/download/DOE-22/Bugfixes-047h.pdf
>
>Question - Do you (or anybody on the list) have any ideas why 
>invoking "INTERMITTENT" in a program that uses DOE-2.1E*V119 would 
>show such effects on heating energy (very, very, very low)?????
>
>
>Thanks for thinking about this!
>
>
>
>
>
>Robert Wichert P.Eng. LEED AP BD&C
>+1 916 966 9060
>FAX +1 916 966 9068
>
>
>
>
>
>
>
>===============================================
>On 1/27/2013 7:47 AM, Chris Jones wrote:
>>Hello Jay,
>>Do you have the DOE2.2 Reference 
>>manuals?  DOE2.2Vol2-Dictionary.pdf explains what the INTERMITTENT 
>>keyword means.
>>
>>See page 361 under INDOOR-FAN-MODE.
>>
>>The reference manuals are available for download at
>>http://doe2.com/download/doe-22/
>>
>>Download the latest edition of each manual and enjoy!
>>
>>
>>At 05:29 PM 26/01/2013, Jay M wrote:
>>>Hi all,
>>>
>>>I tried searching for an answer on archives but unable to find an answer.
>>>
>>>I in Schematic Mode I set fan to "intermittent"  meaning HVAC fan 
>>>is only on when heating/cooling is needed...
>>>
>>>1) if I set it a value of "1" fan is on alwayst on
>>>2) Set 0 Fan is "off"
>>>
>>>Since it is in intermittent mode, when i set to 0.... there is 
>>>never any cooling.  what am I doing wrong?  Because if i set fan 
>>>schedule in Detailed edit mod to 1 the fan is always on and I don't want that.
>>>
>>>I want intermittment fan schedule  but it's either 1 or 0 in the 
>>>fan schedule...
>>>
>>>
>>>Thanks!
>>>_______________________________________________
>>
>> >>
>>Christopher Jones, P.Eng.
>>Suite 1801, 1 Yonge Street
>>Toronto, ON M5E1W7
>>Tel. 416-203-7465
>>Fax. 416-946-1005
>>email <mailto:cj at enersave.ca>cj at enersave.ca
>>
>>
>>
>>_______________________________________________
>>Equest-users mailing list
>><http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>To unsubscribe from this mailing list send  a blank message to 
>><mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
 >>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130127/c45d92c1/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list